Roger

Hi there,just started and came across my first problem.

I have completed some work to get some experience and will do all the necessary tests to verify it is installed correctly,still buying my equipment (blimey there's loads) Its only simple stuff well I thought it was simple.Its a existing garden lighting circuit using 4 core amoured cable.I will try to explain ,the cable is feeding 3 sodium lamps through a timer clock using one live (brown).The other live feed goes to 2 pillar lights(grey) it has a single light switch which goes through a dusk/dawn sensor.The live feed for it all has been taken from a MCB in 1.5 twin/earth and the live is just feed to the clock switch and then onto the light switch.Neutral and earth are shared.I isolated the circuit and disconnected the pillar lights as that was what i was replacing.To doulble check cable route and which was the right feeds I put my fluke across the terminals and when circuit was live I have a voltage of 28.5 on my grey live with the light switch CLOSED ! when switched on I got 242 volts.Circuit seems to check out ok but the amoured cable is not all buried so I think it might be a short somewhere.Any ideas ?
Also found the kitchen fitters whilst hanging cupboards drilled the ring main and bodged with crimp terminals and plenty of tape,quality piece of work !!!!! and every time i pull a soket off at least one wire seems to pop off ! is this normal.

And one more thing where is the Best place for Seaward and Meggers in Surrey ?
Cheers,
 
Can you confirm something for me did you say Neutral and earth are shared :O in this armoured????
 
To clarify the amoured cable is 4 core steel amoured 2 lives and one neutral and one earth.The different lights being feed by different lives.All lights use the same neutral and earth connections,seperate wires.
 
I get you now, if as you say your testing across an open circuit and seeing a voltage its highly likely you are just getting a bit of induction due to the wire you are testing running in parallel to the feed to d/d sensor you could try doing this test after removing power to the second feed to confirm, if you disconnect the d/d sensor and lights and do an insulation test to confirm swa is ok just to be on the safe side.
The acme repair is a no! no! and needs a professional approach.
 
Last edited by a moderator:
I had a feeling that was what was happening as reading some similar posts regarding strange volatge issues.My insulation tester arrives Monday at the wholesaler so will check the swa.
I had repaired the kitchen fitters lash up but putting in a proper junction box in.
Many thanks for your help wil let you know the outcome,you can not sleep either!
 