If a fork lift has already hit it then placing out of reach is somewhat tenuous and a means of protection I have never resorted to in 40 odd years.
 
Years ago it was not uncommon to install private overhead lines for distribution circuits in places like farms, caravan parks, industrial sites.

It may be that these days it is no longer suitable for that site and it could attract a C2 code should an EICR be carried out. But this shouldn't have any bearing on you installing a fire alarm.
 
If a fork lift has already hit it then placing out of reach is somewhat tenuous and a means of protection I have never resorted to in 40 odd years.
Farm lads around here run into LV overheads all the time, seems ‘placing out of reach’ was never really considered with 20’ flail mowers in mind!!
 
I'm picturing LV overhead lines feeding a 3ph DB in a barn (BS 6181's) and in turn from there feeding another 3ph DB.
just a pole with 5 horizontal lines 3ph N E . Which go across to, two other poles , between old barns , then a phase dropped down to one board and 3 phase supply dropped down to another fused board , SWA used from the lines down to the boards. All protected by 32amp 60898 with linked 61009 RCB0.
And SWA cables feeding other 'boards' !! from the overhead lines ........ but where is the metering unless it is a private distribution network and metering is at source/intake? and whole lot protected by 32A mcb?
 
This sounds to me like Barns with the customers overhead connections after the intake and metering.
There used to be many like this near me, with uninsulated conductors running on poles between the Barns.
Most of them now have been changed to underground supplies due to the exact problem above.
As tractors and equipment has got bigger they have become more likely to be struck by such equipment and as a result installed in a much safer way!
 
And SWA cables feeding other 'boards' !! from the overhead lines ........ but where is the metering unless it is a private distribution network and metering is at source/intake? and whole lot protected by 32A mcb?

Yes, relatively common, especially in rural areas, once upon a time.
The bare overhead lines would be hard-drawn copper and supported on porcelain insulators.
PILC, SWA or insulated and sheathed tails would be connected to them via line taps wherever required.

I suspect this type of distribution is the reason, or at least one of the reasons, that 'placing out of reach' is still in the regulations as a method of protection.
Much like BS3036 fuses and PEN conductors, you can't just remove the regulations that support them because they still exist in the real world despite being out dated.
 
This thread hasn't been replied to for 14 days, so replying to this one may not get a response. Post a new thread instead.

Reply to Supply question in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

  • Question
Replies
3
Views
324
  • Question
Replies
10
Views
412
  • Question
Replies
9
Views
823

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top