Looks good. What is the problem with using a stat and airflow?
Sorry, nothing. Everything that has been said I support. The unit is not designed to do what the customer wants i.e. its and intermittent fan. Also wiring a fan to a stat would be good as well as ensuring there is airflow into the cupboard.

Hope that clarifies what I was trying to say?
 
What about one of these 2 uploadfromtaptalk1469730370944.pnguploadfromtaptalk1469730375971.png
 
Make sure you wire the stat to make rather than break on temperature rise - the opposite to a central heating thermostat.

What stat would you recommend for this job - I need to do the same thing in my attic room, have wired ready but don't know much about thermostats. The changeover contacts - are they possible to reverse to make not break on all stats. Thanks


Sent from my iPhone using Tapatalk
 
What stat would you recommend for this job - I need to do the same thing in my attic room, have wired ready but don't know much about thermostats. The changeover contacts - are they possible to reverse to make not break on all stats. Thanks


Sent from my iPhone using Tapatalk
This is the one I've been looking at.
uploadfromtaptalk1470603855834.png
Not sure how good it is but downloaded the data sheet and it shows how to wire it for both heating and cooling.
Hope that helps.
 
Thanks sparky1508 - the changeover contacts is the relevant bit.


Sent from my iPad using Tapatalk
 