Dec 20, 2012
371
128
118
Newcastle
Hi all, just wondering where i stand here. Scenario is as follows PME supply, 60a service fuse, 16mm tails running into DP isolator in the meter box. Going to upgrade the CU,no problem with load etc so the 60a fuse is fine. Was going to run new 25mm tails into the Dp isolator. Do the tails from the other side of the isolator need to be upgraded too? Like i say, service fuse and load aren't changing, obviously the 16mm is fine, but wasnt sure if it would need to be changed from the meter to the isolator. Cant pull service fuse so if it needed done the energy supplier would have to do this and probably charge for it yes??
 
No, so long as tails are in good condition they don't need to be upgraded. Same goes with isolator->CU tails - why are you upgrading them if they're in good condition?
 
No, so long as tails are in good condition they don't need to be upgraded. Same goes with isolator->CU tails - why are you upgrading them if they're in good condition?
Its for an assessment an even though we all know that is fine to use the 16mm, OSG stating 25mm tails be used, i just dont want any over zealous assessor giving me a hard time about it.
 
Its for an assessment an even though we all know that is fine to use the 16mm, OSG stating 25mm tails be used, i just dont want any over zealous assessor giving me a hard time about it.

Where does the OSG state 25mm tails should be used and which regulation does it reference ?
 
514.3 is concerned with the identification of conductors. There is no reg that backs up the assertion that 25mm tails must be used.

Anyway, back to the question. The meter tails (between meter and isolator)are the concern of the supplier. Even if you get in touch with them asking to upgrade them to 25mm, if they don't see a reason to they won't, and there won't be a reason to.
 
  • Like
Reactions: TheCodboy
OSG is a guide, BS 7671 is the book you work to and that says no such thing.

Also, if it's for assessment, one thing he will pull you up on is no KMF for meter tails over 3m.
 
OSG is a guide, BS 7671 is the book you work to and that says no such thing.

Also, if it's for assessment, one thing he will pull you up on is no KMF for meter tails over 3m.
Tail length is fine,coming straight,through from outside meter,up the wall in trunking, secured with fire clips (maybe a bit of overkill).
 
514.3 is concerned with the identification of conductors. There is no reg that backs up the assertion that 25mm tails must be used.

Anyway, back to the question. The meter tails (between meter and isolator)are the concern of the supplier. Even if you get in touch with them asking to upgrade them to 25mm, if they don't see a reason to they won't, and there won't be a reason to.
Nice one, Thanks for the info!
 
If you are worried about Inspector Gadget, perhaps a comment on the cert, "16mm tails Ref Method B/C in good condition but will need review if service fuse is upgraded from 60A". Then you'll have answered the question before it's asked.
 
If you are worried about Inspector Gadget, perhaps a comment on the cert, "16mm tails Ref Method B/C in good condition but will need review if service fuse is upgraded from 60A". Then you'll have answered the question before it's asked.

I wouldn't be extra sure that Gadget himself doesn't worship the "Gospels according to the On site guide"
 
If I waa an ---, which I am and if I waa assessing you which I am not I may ask why you left the 16.0 tails in. The only reason would be to confirm you understand why they didn't need changing which they do not.
 
Not a 3036, 60A fuse is it might change my mind on that.
 
That reference in the OSG stinks of dumbing-down to me, almost like they are saying, well if we try and make everyone put in 25mm^2 tails, then folk can't get it wrong, and it doesn't matter if they don't know what they're doing.
 
Going back to the charge for the upgrade, If you tell the DNO you expecting to fit an electric shower or induction hob they will upgrade the fuse to 80A and should do the tails at the same time.
 
  • Like
Reactions: TheCodboy
  • Like
Reactions: Wilko

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

TheCodboy

Arms
~
Joined
Location
Newcastle

Thread Information

Title
Tails from meter to DP isolator
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30

Advert

Thread statistics

Created
TheCodboy,
Last reply from
7029 dave,
Replies
30
Views
5,172

Advert