Re: Tell us about your faults !

"Don't you usually get some leakage from old boilers"
Lilets or bodyform sort that type of bother
 
Re: Tell us about your faults !

How many types of cable can you fit in a meter, lead sheath, VIR, T+E, I Peed myself laughing when I saw this, the customer didn't get why lol:D

View attachment 5804

I once knew a fella that ran a 3ph machine in his shed. He used his phase then pinched the other two off his neighbours in henly blocks. Time served EITB spark as well.
Absolute bloody genius!!!
 
Re: Tell us about your faults !

Right same job as the meter pic above, fuses in the neutrals and antique boards :D, the owner is 92 and doesn't fancy the rewire.:)

photo-93.jpgphoto-94.jpg
 
Re: Tell us about your faults !

Just checked out a small job,customer having cutout moved on tuesday by the local supply company
When checked the sevice found to be pme but then found that there was over head supply Comming in that changed it to TT
Problem is sevice is bonded neutral to earth and also a earth electrode but no Rcd ?

Lost
 
Re: Tell us about your faults !

well i had my rcd tripping continously but then i found that there was a loose connection on the cable tied to the mother inlaws metal chair it was close but fixed now !!
but i got this foul smell coming from her room any ideas!!!
 
Re: Tell us about your faults !

thanks buddy did not think of that solved it now she,s smelling a bit but i suppose they are all like that at thier age
 
Re: Tell us about your faults !

Try a bucket water this some times helps it along may be some time before smell will go

Happy days
 
As we speak now I'm in a bathroom changing a fan... Customer says the old one works but doesn't seem very effective.. Mmm let's see....
d4b78068-9551-f5e0.jpg


d4b78068-9572-5b5c.jpg


d4b78068-9595-1aed.jpg
 
Re: Tell us about your faults !

Guy in the unit next to me asked for some help. He was having a problem with the main trip that kept tripping. A 'sparks' had wired up his 9.7kw water heater via a new piece of 6mm , that went in to a switch, came out in 4, then hidden out of sight into 1.5 and into a 6amp trip. Hidden on top of one of the kitchen cupboards was the instructions, which said many helpful things including something about 45 amp breaker!!
 
Re: Tell us about your faults !

Got called out to a house where: they were getting shock from shower while standing in the bath, the rcbo for kitchen circuit constantly tripped out, and some lights glowed a little even when switched off.

On investigating inside CU I found I had no voltage between L & E, although still had 240 between N & E and L & N. In the end I concluded that I had a live incoming earth (TNS supply)! Seemed to me this had to be the result of 2 faults on supply side - one to break the earth continuity back to sub-station, and one nearer the property to connect the live supply to earth - otherwise sub-station fuse would have blown.

I disconnected earth, put in earth rod an connected up as temporary TT, and told customer not to touch the earth until DNO had been as I couldn't think how I could disconnect it. Just glad I hadn't touched the earth as it was live back to sub-station fuse!

btw - DNO did find 2 faults - one each side of the front garden wall
 