Testing during a consumer unit change

I do a full EICR before the board is removed from the wall.

Do you charge that separately, or is that inclusive of the price for a CU change?

I only ask, as some, for an EICR, appear to charge fixed price & in addition price per circuit?

As we're in open forum, lets say a silly price of £500 & £50 per circuit for the EICR, then £1000 for the CU change (normal 3 bed domestic property, dual RCD CU).

I just used just charge the £1000. However, I'd carry out some suitable testing, the day or so before.
 
You’ll need to test the tails being connected to the new CU.
Inspect the earthing and bonding to ensure they are adequate.
Test any RCDs or RCBOs you install, and test any circuits below 16A to ensure Zs is low enough. Unless of course, the board you are changing has MCBs.
Which out for borrowed neutrals on the lighting.
 
Agree with above...do the obvious,like so many as said,offer a full Eicr,with DB change,if not basic testing.
If you’ve got tight arse people,it’s gotta be better than it was when originally installed.
 