Hi all I am currently on a site and just pulling some data in the plant room and noticed this :-

Main LV panel
3 phase breaker rated 125amp with 25mm non armoured tails and 16mm earth supplying landlord board run in trunking with 27 other swa 16mm 3core

Then off the 3phase bus bars we have 3x 250amp 3phase breakers with 25mm non armoured tails running off to 3 seperate 3phase boards supplying 11apartments from each board split over 3phases again with a 16mm earth and run in with 27 other 16mm swa 3 core supplying the sub boards protected by a 63 amp breaker.

My understanding is that a 25mm single core non armoured cable 3phase run in trunking can only hold top end of 80amp (not sure of exact top of my head)

And same again with 35mm can only take 110ish in same situation...

Any thoughts?
 
the rating of the breakers is irrelevant as long as they,re rated high enough for the load. the only thing of concern is the OCPD ratings being correct for the cables which they protect. (In<Iz).
 
oops, misread part of the OP. didn't see that you'd put 250A breakers. the 25mm tails should be protected by no more than 100A breakers. are they deffo breakers and not isolators?
 
Seems a little strange that these MCCBs are so overrated for the cables they are protecting. The only other thing i can think of (if these breakers are not oversized) is that many get confused by the printed label frame size, for the actual rating size. As it's often the case, that the rating size is indicated in much smaller print

Anyway if what you are saying is correct, then i can't see why you wouldn't bring your observations to the notice of the responsible person for this installation....
 
It goes 400amp main isolator, then bus bar, then tapped off bus bar what looks to be manufacture tails 35mm from each phase supplying 3 3phase 250amp mccb's then 25mm no armoureds through trunking to 3 seperate 3phase dis boards.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Thoughts on plant room do I speak up?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
p11jor,
Last reply from
polo1,
Replies
11
Views
1,738

Advert

Back
Top