According to BS 7671, (411.4.4 Note 1), on TN C systems it is prohibited to use RCD protection.Could someone please explain why???
Background info is: Small industrial unit supplied by a TN C system. DB then splits to supply a set of offices and toilets via a 6 way domestic CU. Client wants to upgrade to a 17th edition RCD protected unit. Would this present a problem ?
 
With TN-C the earth is combined with the neutral, This means that an RCD will have no way of seeing the inbalance between earth/ Neutral should a fault develope.

TN-C is a rare combination these days so check it really is that kind of earthing arrangement.
 
Gamm to tell the difference you have to find where the neutral and earth split. Is it before or after the meter?

If its before its a TN-C-S if its after at the Main D.B ther will be a Link betwenn Phase and Neutral. TN-C
 
Lister TNC systyems have to be "Under supervision of a competent person" so you dont have to use RCDs . They are also thankfully very rare.

Have a look at 411.4.1 its pritty clearly worded that no rcds on a tnc system.

In that system its down to the sparks to ensure the ZS is low enouph for disconnection times by either supplimentary earthing, use of overcurrent devices. for example HRC fuses instead of MCBs you have to be VERY CAREFULL.

I would try and change the earthing system to TN-C-S myself if possible.
 
Thank all that have responded to my dilemma, I havnt checked the system myself, but client produced an 11 year old EIC which clearly stated system type : TN C. I will drop by today and look for myself and post result tonight.:(
 
Update as promised: The TN C system turned out to be TN C S so no probs with the RCDs. Thanks again to all who responded.:)
 
To add to this.. I think i may have come across a TN C system. Would like some advice is possible. After taking a peek in the meter cabinet i noticed a strange layout that i cant say ive seen b4. This had a yellow sticker on saying "WARNING This installation is connected to a network with protective multiple earthing Please consult YEB regarding earthing?. Have some pictures but will need to upload from my mobile when i get the chance..
 
Last edited by a moderator:
Agreed, sounds like it's a TN-C-S (PME).

It is very rare to come across a TN-C system particularly in a domestic situation for the simple reason that you cannot use RCD's.
 
muikeymoo PME is also known as TN-C-S lets see the photos to prove it though

Isnt TN C also known as PME? Will upload pics.
The installation is approx 28 years old if thats a clue. When would you normaly find a TN C system? Was it used just to reduce the risk of broken neutrals?
 
Last edited by a moderator:
Thanks for the link mate.. From info, if i were to take alook inside the cu and the earth and neutal are seperate then its TN-C-S? because in TN-C system its combined throughout??


Just phoned YEDL tec helpline and can you believe it they dont hold info regarding the earthing arrangments!!. And wanna relieve me of £150 to come fit an earthing block. Also to add insult to injury will take 6-8 weeks!!. Whats the crack with me adding the earthing block myself?? Will get around to unloading those pics today so if someone could take a look i would be grateful.
 
Last edited by a moderator:
If you look at page 32 of the big red book you are NOT allowed to use a TN-C as a consumer under ESQCR Regulations 2002.

The DNO can supply you via this way but then it must split at the point of intake giving the cosumer a seperate earth and neutral.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
TN C system. RCD ???
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Gamma,
Last reply from
mikeymoo,
Replies
15
Views
17,703

Advert

Back
Top