Evening all.
EICR done on ground floor flat all electric no gas, flats built 2006, no rcd protection on circuits 1 to 8 - lighting, kitchen appliance sockets , immersion ,panel heaters and towel rail, 3 storage heaters via contactor and rcd control 2nd immersion, general sockets, all cables installed within metal stud plaster boarded walls, 3 points that are visible show no grommets and butchered holes in metal frame with cables down to accessories , no supplementary bonding through out bath room. All insulation readings clear as a bell.

C2 no rcd protection on towel rail, bath room light and fan, shaver point and cables within metal stud,
Or C3 improvement

Thanks all in advance
 
C2 for no RCD for any bathroom circuits where there's no supp.boding.
C2 for cables in metal stud with no RCD.
C2 for kitchen sockets, no RCD.
C3 for no RCD lighting circuit/s.
 
C2 for no RCD for any bathroom circuits where there's no supp.boding.
C2 for cables in metal stud with no RCD.
C2 for kitchen sockets, no RCD.
C3 for no RCD lighting circuit/s.
Cheers Tel.
DB change then , told me gaffa this and was told it was wired to previous regs so it passes 14 apartments wired like that. Am I right in saying early 17th edition regs .
 
late 16th. irrespective of whether it complied the, your EICR is to determine if anything is dangerous or not. you inspect to current regs. any C1 or C2 issues must be rectified to get asatisfactory report.
 
Cheers Tel.
DB change then , told me gaffa this and was told it was wired to previous regs so it passes 14 apartments wired like that. Am I right in saying early 17th edition regs .

Your boss had a worrying outlook. How many other 'successful' EICRs has he done like this I wonder?
 
The Best Practice Guide #4 covers many of these points:
https://www.----------------------------/professional-resources/best-practice-guides/

But as @telectrix said you consider it relative to the current regas and code any discrepancies based on the sort of risk they present from C1 to C3.

For an installation that is good to its original standard then the usual issues are the lack of RCD protection, the risk from that of course depends very much on the details of what the circuits are and where they power. But also the occasional unexpected points such as immersion heaters without a safety cut-out thermostat to BS EN 60335-2-73
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Stafford
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
To change DB or not ?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
6

Thread Tags

Tags Tags
change

Advert

Thread statistics

Created
Stevie g,
Last reply from
Stevie g,
Replies
6
Views
1,779

Advert

Back
Top