Had a look at a fault for a mate, cooker kept taking out main 30mA rcd when switched on at cooker switch (no load, just turning on at wall)

Disconnected cooker, turned on all ok. Cooker faulty? Had it tested and it was fine.

Tested circuit, megger, r1+r2, all perfect. Went to do zs and got a reading of 460ohms!

Checked ze at db and was very similar, did ramp test on rcd and its tripping at 15mA.

Traced the 10mm earth (all surface clipped) and it disappears under a paving slab.

Will having a high ze cause the rcd to operate early or not?

I'm going to install a new earth road in the week, will try and get hold of a General Electric main switch/rcd but im not sure who would get hold of one?

Cheers

Ash
 
Last edited by a moderator:
High Ze more likely to make it fail to work. If it's threashold is 15mA then bin it and replace it anway, then start testing again. You often find that the RCD is the cause of the high Zs IF the Ze is OK (but not in this case).
 
Had a look at a fault for a mate, cooker kept taking out main 30mA rcd when switched on at cooker switch (no load, just turning on at wall)

Disconnected cooker, turned on all ok. Cooker faulty? Had it tested and it was fine.

Tested circuit, megger, r1+r2, all perfect. Went to do zs and got a reading of 460ohms!

Checked ze at db and was very similar, did ramp test on rcd and its tripping at 15mA.

Traced the 10mm earth (all surface clipped) and it disappears under a paving slab.

Will having a high ze cause the rcd to operate early or not?

I'm going to install a new earth road in the week, will try and get hold of a General Electric main switch/rcd but im not sure who would get hold of one?

Cheers

Ash


The answer to your question is no, having a high Ra and consequently a high Zs (460 Ohms is not abysmal on a TT system if it is fairly constant and has 30mA protection) will not cause early operation of the RCD.

I know you say you had it tested but my money is still on a cooker fault (maybe intermittent).
 
The cooker was taken away to a specialist for testing and a replacement dropped off while it was away. The replacement also caused tripping problems. Doesn't do it every time just randomly!

Any suggestions on where to find a GE 30mA 80a DP RCD? or will an alternative fit?
 
The answer to your question is no, having a high Ra and consequently a high Zs (460 Ohms is not abysmal on a TT system if it is fairly constant and has 30mA protection) will not cause early operation of the RCD.

you say you had it tested but my moneI know y is still on a cooker fault (maybe intermittent).

Not with an RCD tripping out on 15mA... As Topquark, says it needs replacing!!
 
Tried google first, can't fine on that looks the same.
eBay has one but it's second hand and I'm dubious about fitting second hand parts.

This is the rcd in question
e93fc60f.jpg
 

Reply to TT high ze - rcd tripping in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
352
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
577
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
911
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock