Had a look at a fault for a mate, cooker kept taking out main 30mA rcd when switched on at cooker switch (no load, just turning on at wall)
Disconnected cooker, turned on all ok. Cooker faulty? Had it tested and it was fine.
Tested circuit, megger, r1+r2, all perfect. Went to do zs and got a reading of 460ohms!
Checked ze at db and was very similar, did ramp test on rcd and its tripping at 15mA.
Traced the 10mm earth (all surface clipped) and it disappears under a paving slab.
Will having a high ze cause the rcd to operate early or not?
I'm going to install a new earth road in the week, will try and get hold of a General Electric main switch/rcd but im not sure who would get hold of one?
Cheers
Ash
Disconnected cooker, turned on all ok. Cooker faulty? Had it tested and it was fine.
Tested circuit, megger, r1+r2, all perfect. Went to do zs and got a reading of 460ohms!
Checked ze at db and was very similar, did ramp test on rcd and its tripping at 15mA.
Traced the 10mm earth (all surface clipped) and it disappears under a paving slab.
Will having a high ze cause the rcd to operate early or not?
I'm going to install a new earth road in the week, will try and get hold of a General Electric main switch/rcd but im not sure who would get hold of one?
Cheers
Ash