Marc13

I have a 3 month old condensing tumble dryer, which has recently started tripping out the RCD (63A, 30mA) within 30 secs of being on. I've tested the RCD, which was going out at 18mA, and the tumble has an earth leakage of 1.17mA. I have now changed the RCD, but still continues to trip, within about 5 mins of running this time though. Any advice? Should I contact the manufacturer?
 
Empty the water out of the condenser haha, JK, have you tested the motor windings to earth?
 
was going to edit my post, but as you beat me too it haha, considering the age I would return the product as faulty if the RCD is tested as okay, thanks Dillb
 
I have a 3 month old condensing tumble dryer, which has recently started tripping out the RCD (63A, 30mA) within 30 secs of being on. I've tested the RCD, which was going out at 18mA, and the tumble has an earth leakage of 1.17mA. I have now changed the RCD, but still continues to trip, within about 5 mins of running this time though. Any advice? Should I contact the manufacturer?

Mine stared doing that, then a couple of weeks ago it caught fire.

I've cleaned it up now & given it to Tidy Boiler .............
 
Probably an element issue but dosn't show until its heated up... its within warranty so as already stated return the goods as faulty, you could confirm by bypassing rcd and clamping leakkage as it runs, you'll probably find it suddenly rises enough to cause a trip.
 
I had a similar problem with an Indiset conenser drier. When the condenser had filled with fluff etc, water would leak in to a resivoir in the bottom of the drier. Over time the resivoir would overflow. The drier fan would then flick the excess water into the heater element, causing a short and tripping the rcd. All I did was clean the condenser, removed the panel from the back of the drier, and dried out the element with a hair drier. Following this, I put an rcd plug on the drier and clean the condenser out monthly. The problem has not occured again.
 
If there's nothing wrong with the appliances you may have to run it off its own dedicated circuit...that's if its not on one?

I could be leaving myself open to some abuse here(ref:am1)....could you not surface run (trunking) a new feed without RCD protection aslong as you label the circuit not RCD protected?
 
wonder whether i should return my condenser dryer under warranty. got it from the council tip 3 years ago for £2 in the lads' tea kitty. filter's a bit iffy now.
 
If there's nothing wrong with the appliances you may have to run it off its own dedicated circuit...that's if its not on one?

I could be leaving myself open to some abuse here(ref:am1)....could you not surface run (trunking) a new feed without RCD protection aslong as you label the circuit not RCD protected?

but it's more than likely faulty and only 3 months old, best to send it back.
 
Why not pat test it, this the only procedure for light at end of tunnel and resolution to what you do next.
Pat engineers 1 electricians 0
 
but it's more than likely faulty and only 3 months old, best to send it back.

Stop shooting me down when im trying to be intelligent :laugh:

to be fair, i forgot/misread about it being 3months old lol - what MDJ said, send the bloody thing back :biggrin:
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Tumble Dryer Tripping Rcd
Prefix
N/A
Forum
Electrical Appliances & Whitegoods Forum
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
Marc13,
Last reply from
Stroppy,
Replies
33
Views
45,614

Advert

Back
Top