As my customer didn't know what double oven they wanted I installed a 40A MCB and 6mm twin and earth. When I returned for the second fix they have installed two ovens. One is a single oven (3.65kw 16A) and the other is a microwave/grill/oven (3.45kw 16A). So what is the best way to connect both with one supply? The first idea I had was to use a 45A DP Switch and wire both ovens to this. Ideally, I would like to isolate each one separately. Has anyone any suggestions?
 
I tend to wire these on a socket and plug top (single socket for each) as one you apply diversity the loading usually drops to below 10amps. Don't know what model you have though could be a particular large single oven ??????? This would mean some kind of joint as sockets won't take two 6mm obviously lol
 
I tend to wire these on a socket and plug top (single socket for each) as one you apply diversity the loading usually drops to below 10amps. Don't know what model you have though could be a particular large single oven ??????? This would mean some kind of joint as sockets won't take two 6mm obviously lol
MK sockets will allow x2 6mm cables
 
I must say I had exactly this situation a few weeks ago, and I put 2 DP switches off the single 6mm cable, one for each oven. However, afterwards I thought it was probably unnecessary, and as Murdoch says a single switch is fine. You have to consider what the switch is for, it only to turn the oven off in an emergency. If one of them fails an electrician will have to disconnect it properly anyway, they are just switches not isolators.
 
Hi Simon - agree above - one switch and a double outlet gets my vote :)
45 Amp Dual Appliance / Cooker Outlet Plate - https://www.tlc-direct.co.uk/Products/AA45DCOP.html

IMG_0778.JPG
 
I take your point but would like to add would never use a plug and socket on anything like a hob or double oven ect just single ovens and combination microwave as these tend to either come with a plug or a piece of 1.5 flex fitted.
Don't wanna sound like a --- but am new here and don't you guys thinking I'm some kinda cowboy yey haw lol
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Electron

Arms
-
Joined
Location
Altrincham, Cheshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Business Name
Simon Linton - Domestic Electrician

Thread Information

Title
Two Ovens, One Cable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
28
Unsolved
--

Advert

Thread statistics

Created
Electron,
Last reply from
Midwest,
Replies
28
Views
20,281

Advert

Back
Top