My builder has sprung a job on me.
New circuit required for a hob.
The CU has a single 30mA RCD, type AC.
I am still unsure exactly when I should insist on type A, and when I should just advise.

Would you guys be insisting on type A in this case, thus fitting a new CU (as it is an old NSB wylex board with an RCD taking up 3 slots (WSES 100/2). Pretty sure there wouldn't be a type A available)).

The MI would be interesting to read, but I don't have them.

Not sure how be are supposed to determine if there is a possibility of pulsating, residual DC.

Thanks.
 
You need to bear in mind what else is on that RCCB, and which could prevent it from operating correctly. It's not just the load you're adding which is relevant - DC from other parts of the installation could render the RCD protection ineffective for your addition/alteration.
 
We should always 'advise', as our recommendations to clients should always be based against current best practice. However, whether we need to 'insist' is an entirely different animal. For example - in the unlikely event that the cable feeding the circuit is surface clipped then there's no need for any RCD in the absence of a MI that stipulates one (assuming no socket outlet on the oven switch....). As already said above, whilst my personal gut tells me you'll be fine to stay on an AC, only you know what you're installing and what's there already. Also, one assumes that there was an existing oven/hob as part of the original install anyway?
 
We should always 'advise', as our recommendations to clients should always be based against current best practice. However, whether we need to 'insist' is an entirely different animal. For example - in the unlikely event that the cable feeding the circuit is surface clipped then there's no need for any RCD in the absence of a MI that stipulates one (assuming no socket outlet on the oven switch....). As already said above, whilst my personal gut tells me you'll be fine to stay on an AC, only you know what you're installing and what's there already. Also, one assumes that there was an existing oven/hob as part of the original install anyway?
You would think there is already one there, but the builder hasn't mentioned this. He's pretty savvy, and I believe he would have mentioned this during our chat if there was one.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Type A rcd for cooker or type AC OK?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
HappyHippyDad,
Replies
4
Views
2,539

Advert

Back
Top