Hi everyone.
Quick question, I hope, as I can't find a definitive answer anywhere.
In order to do an alteration/addition to existing circuits on a PME system do the meter tails and main earth conductor need upgrading from 16mm and 10mm respectively?
Western Power engineers have told me 25mm tails are only required on new installations.
Also if they are not upgraded should it be noted on the eic as a departure from BS7671 or a comment on existing installation??

Thanks in advance.
sjm
 
If they are existing and the fuse rating is 60 amps and the maximum loading is less than the current carrying capacity of the 16mm then all should be ok ,although on a PME TNCS the main earth should be 16 mm if im not mistaken
 

Reply to upgrading meter tails & main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock