A
amberleaf
form one Electrician to another hope this helps some were , please tell me ? Test 1
Adjust the current setting on the test meter to 100% of the rated trip current of the RCD and perform a test. !! This has be Replaced , ( OLD ) ↔ A general purpose RCD BS4293 !! should operate within 200mS ← . A general purpose ( OLD ) RCD BS4293 ↔ RCD BS-61008 ( New ) or RCBO to BS-61009 should operate within 300ms ← *
Test 2 An RCD provided for Basic Protection should have a rated TRIP current not exceeding 30mA If the RCD is rated at 30mA , adjust the current setting on the test meter to 150ma ( x5 ) and perform a test. The RCD must operate in a time not exceeding 40mS. *
Test 3 Adjust the current setting on the test meter to ½ ↔ 50% of the RCD trip current and perform a test. The RCD should not operate within 2 seconds
The Test Button : Finally operate the RCD by pressing its test button
RCD test Procedure ,
1 , Within 200mS for non delayed being one reason.
2 , Delayed being 300mS to 400mS allows better chance discrimination over a downstream 200mS device than a 130mS to 500mS might do over a 300mS device being another reason
Furthermore a factor of three of the tripping current should also be provided for discrimination i.e.
usually a delayed 100mA feeding a non delayed 30mA trip or ,
RCDs in Series : 531.2.9 ←
A BIG BIG thank you , that's all I was asking for to help other Electricians This City & Guilds 2392-10 Course is New to a lot of spark's it is a Minnie version of 2391( follow on )
I,LL send the boys down form Scotland if you don't keep your word I,ll be watching this SPACE , Freedom , Big Thank You