as above and you will find on the boiler that there is a 230 volt switch live
for the underfloor heating manifold, i was told that those volt free contacts you can supply 240 volts into one side of and take another out of it ( like a light switch) is that right???
 
as said DO NOT put any voltage on to volt free contacts, you will need a volt free stat or the like to work it
 
as said DO NOT put any voltage on to volt free contacts, you will need a volt free stat or the like to work it

so why does the diagram physically show a "L" going into that "volt free connection then on that underfloor heating manifold??
 
Yes that's right, the RHS top section shows the L & N being fed into the board, then the boiler and pump relays which are volt free, can be looped off to feed the Live side and switched internally.

In the case of the boiler, the manufacturer is calling R & P volt free, as some do? But there will more than likely be a neglegible voltage to drive a 4 - 20 ma current to switch or signal a component on the pcb.

As previously commented, check the voltage with a bench meter, or short out the i/p and o/p and see if you get a function?
 
Yes that's right, the RHS top section shows the L & N being fed into the board, then the boiler and pump relays which are volt free, can be looped off to feed the Live side and switched internally.

In the case of the boiler, the manufacturer is calling R & P volt free, as some do? But there will more than likely be a neglegible voltage to drive a 4 - 20 ma current to switch or signal a component on the pcb.

As previously commented, check the voltage with a bench meter, or short out the i/p and o/p and see if you get a function?

yea i thought i was right about the underfloor heating manifold, so if i was too loop of the live side to one side of the "volt free" connections, i assume then i will take a switch wire from the side of that switch to the boiler and pump is that correct???
 
Yes on the Myson wiring centre, but the R & P on the boiler will just need shorting by the microswitches on the zone valves.
 
Thank you very much, i knew i was right about that, don't know why that other guy was telling me different ...
 
I was telling you different because I believe you are wrong (mainly because it says about 10 times do not put a voltage across) I was trying to find a link for you but could not. Do yourself a favour tomorrow and phone the tech line If I am wrong you have lost price of a phone call. On every boiler I have ever done there has been volt free and 240 side but your call.
 
I was telling you different because I believe you are wrong (mainly because it says about 10 times do not put a voltage across) I was trying to find a link for you but could not. Do yourself a favour tomorrow and phone the tech line If I am wrong you have lost price of a phone call. On every boiler I have ever done there has been volt free and 240 side but your call.
Well that other guy told me right there, so it must be true, and I've heard that's how it's done as well you can apply 240v to that volt free connections on the underfloor heating manifold
 
Just because the underfloor heating diagram points to that has nothing to do with your boiler, but I am not trying to make life hard, as I said your call.
 
Kev, they'll be tears if you put 230v on those contacts. The underfloor heating has nothing to do with the boiler you're working on and just to clarify the situation (as I see it) volt free inputs (I/P) are just that, for the likes of normally closed (n/c) or normally open (n/o) contacts (basically signals provided internally) on the other hand (as found on the underfloor heating you mention) volt free outputs (O/P) are normally open (n/o) contacts for you to supply a voltage (in this case 230v) to feed whatever that needs feeding (can't be bothered going back and having a look, but could be a fan, light, pump etc!)
I hope that makes some sense.
So take the advice given before you damage anything!
 
I was browsing about the internet there, and i noticed you could use a relay to provide volt free contacts to a boiler how does that work? when there is 240v supplying the coil ???
 
Voltage free contacts is a term given to contacts which you apply your own voltage signal, or signal or 4-20ma etc.
Voltage free contacts as in a relay or microswitches will be rated and shown with max amps and max voltage. IE 2amp/230v or 24volt dc/5amp etc etc.
This boiler manufacturer seems to have used unfortunate wording in their description of R and P. I read it like has already been stated and is 4-20ma (with 10 volts to carry it) or 24volt etc. Looks to me like they have had a lot of returns/faults which are site based and so the emphasis on warning after warning.
The easiest to explain it is if you think of P as power (leaving the boiler at whatever voltage) and R as return (going back to tell the boiler to go). Therefor self contained and no voltage to be applied by your wiring.
 
The voltage only appears across the coil, the contacts are independent.

okay so i could feed the coil with 240volts and take a two core from the relay contacts to the boiler is that correct yea, and that will provide "volt free" contacts to the boiler correct yea??
 