hi all
im currently doing some testing on a university the install is metal trunking and metal conduit used as the earth for the whole installation. when we disconect neutral and carry out isulation resistance test we are getting a 12v between live and the earth bar, and our metrel tester wont allow us to carry out the test. does any one have any ideas.
thanks in advance
 
as spin says, induced volts. need to isolate other circuits while testing.
 
I would imagine, that your tester isn't allowing any tests, because the neutral has been disconnected, or you've altered the settings.
Should allow testing with voltage up to 50V, I believe.
 
long shot, but have you tried using an insulated screwdriver to press test? I had a metrel that would never carry out EFLI tests unless i did this, A symbol saying "phase voltage on PE terminal" came up and it beeped alot.
 
We can't isolate the whole db because some of the circuits are in use so we do what we can there are 17 boards to do so just do what we can wen we can
 
Seems to be I've just been having a read on Internet.do you know where I could find more info on this
 