I have a few pictures that I will attach later but basically the output of the optimiser is at 383V L-L and the fitting ballast states 240V +/- 6% lol.
I notice on the optimiser it states 3Ph 3Wire not four wire. Where’s the neutral coming from for the output?
If the neutral has been simply linked across from the incoming there will be all kinds of problems with voltage imbalance.
Anything with a CE mark on it made from 1990 can be run on 220V. If the voltage is below this, it is automatically is going against manufacturers instructions!
Basically the Optimisers are a big dimmer switch, and they always work without any problems lol.
As said above, get the lighting circuits off the Optimisers. End of re-lamping every week. Good luck Sintra.
As for the lower than normal/expected voltage (optimised voltage) at the lighting fittings, this could well be down to the cable size used and the length of circuits involved. Which is always going to be a factor when retrofitting a voltage optimisation unit into an existing installation.
From the schematics I’ve found I don’t think these are intended for Ph&N use.
To my surprise it is a Y autotransformer with a high impedance part of the winding reversed to form an artificial star point.
With the tertiary, nine windings in total.