We had the same problem with discharge lighting in a warehouse (We didnt install the optimizer). High lamp failures and similiar voltage readings to you. Some manufacturers wouldn't even strike at all, some would.

In the end we turned it into bypass at the client request. It wasnt saving them any money anyway. About 5 years since and no more problems.
 
I think I will suggest that to the client to either bypass the thing or turn it up a few notches.
 
If you check the manufacturer /label of the ballasts then you should be able to find out the minimum voltage that is permitted at the lamp , if you then measure the actual voltage at the lamp connection points, if this is less than the given value you have your answer.
 
Can you get info like make and model of the optimisers. I'd start by putting a scope or a tester with a wave analyzer on the output and check the wave shape and RMS value etc. It could be the reduced voltage but it could also be something waveform related.
 
If you check the manufacturer /label of the ballasts then you should be able to find out the minimum voltage that is permitted at the lamp , if you then measure the actual voltage at the lamp connection points, if this is less than the given value you have your answer.

That's what I was thinking. Will post back tomorrow.

Can you get info like make and model of the optimisers. I'd start by putting a scope or a tester with a wave analyzer on the output and check the wave shape and RMS value etc. It could be the reduced voltage but it could also be something waveform related.

Can get make and model ok. As for a tester I would need to hire one in lol.
 
I have a few pictures that I will attach later but basically the output of the optimiser is at 383V L-L and the fitting ballast states 240V +/- 6% lol.
 
Hmmm, maybe it is a voltage issue then. Where I am the standard voltage is 380/220, it's not uncommon to see only 210v at the load but most European items run fine even though it's at the lower end of their voltage tolerance.

With problems like this I'd be tempted to bounce it back to the customer and tell them to sort it out with the designers of the optimisation installation.
 
Well here are the pics of this stupid box and ballast rating. Looking at the data plate it seems to be set to 5% 380V so turning it up a bit is not an option.
 

Attachments

  • image.jpg
    181.4 KB · Views: 39
  • image.jpg
    170.3 KB · Views: 32
  • image.jpg
    144.3 KB · Views: 31
  • image.jpg
    194.6 KB · Views: 36
  • image.jpg
    222.2 KB · Views: 33
Anything with a CE mark on it made from 1990 can be run on 220V. If the voltage is below this, it is automatically is going against manufacturers instructions!

Basically the Optimisers are a big dimmer switch, and they always work without any problems lol.

As said above, get the lighting circuits off the Optimisers. End of re-lamping every week. Good luck Sintra.
 

Reply to Voltage optimisers and lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
768
Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
We are currently renovating an old house after recently moving in. Whilst purchasing the property we received written assurances that the original...
Replies
47
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock