Maybe i'm missing something here, but all that unit seems to be, is a straight transformer rather than a regulated voltage optimisation unit!! I'd want to see far better output regulation than what's being shown here. If the whole idea is to optimise voltage to 380/220 V then that's what i'd want to be seeing on the output.... The optimisation units that i've had a look at on the Web have a wide'ish tolerance of the input voltage. that can still output a regulated 380/220 V with a very small +/- tolerance.

As for the lower than normal/expected voltage (optimised voltage) at the lighting fittings, this could well be down to the cable size used and the length of circuits involved. Which is always going to be a factor when retrofitting a voltage optimisation unit into an existing installation.
 
Last edited by a moderator:
I notice on the optimiser it states 3Ph 3Wire not four wire. Where’s the neutral coming from for the output?

If the neutral has been simply linked across from the incoming there will be all kinds of problems with voltage imbalance.
 
I notice on the optimiser it states 3Ph 3Wire not four wire. Where’s the neutral coming from for the output?

If the neutral has been simply linked across from the incoming there will be all kinds of problems with voltage imbalance.

Yep i was going to mention that myself... but the post kept posting up. before i was finished writing!! As was also going to advise getting back to the manufacturers. Really need a schematic drawing and a working data sheet (cant think of the correct name?? lol!!)
 
An interesting read, I found the technical data sheet.


  • An unreferenced star output.
  • Tertiary delta winding for harmonic filtration.
  • From what I can make out Fixed input taps.

It’s just a Y∆Y transformer with no active voltage regulation I can see. Had it been a Y autotransformer then the star point would be referenced.

No wonder it’s causing problems. I would only use it for balanced 3Ph loads. I wouldn’t be keen on it then due to problems of L→N faults.

The problem with YY transformers is they are virtually transparent to harmonics hence the tertiary winding.
 
From the schematics I’ve found I don’t think these are intended for Ph&N use.

To my surprise it is a Y autotransformer with a high impedance part of the winding reversed to form an artificial star point.

With the tertiary, nine windings in total.
 
Anything with a CE mark on it made from 1990 can be run on 220V. If the voltage is below this, it is automatically is going against manufacturers instructions!

Basically the Optimisers are a big dimmer switch, and they always work without any problems lol.

As said above, get the lighting circuits off the Optimisers. End of re-lamping every week. Good luck Sintra.

Not easy to get the lighting off the optimisers lol. Optimisers are in switch rooms feeding directly into a 400A panel. Then from this panel the sub main circuits are taken to local dist boards.
 
As for the lower than normal/expected voltage (optimised voltage) at the lighting fittings, this could well be down to the cable size used and the length of circuits involved. Which is always going to be a factor when retrofitting a voltage optimisation unit into an existing installation.

I have to agree that I don't think any thought has gone into the installation of these "optimisers". All final circuits have been properly designed and installed and as I say no issues up until these where fitted.
 
From the schematics I’ve found I don’t think these are intended for Ph&N use.

To my surprise it is a Y autotransformer with a high impedance part of the winding reversed to form an artificial star point.

With the tertiary, nine windings in total.

Thanks Tony for your input. At least I can go back to the client with something a little more concrete than my original thoughts.
 

Reply to Voltage optimisers and lighting in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
769
Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
We are currently renovating an old house after recently moving in. Whilst purchasing the property we received written assurances that the original...
Replies
47
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock