Came across a supply for a 3 phase delta water pump at a friends farm the other day, the cable appeared too small at 2.5mm swa given the distance (1/4 mile) so far as I was concerned. The 25A 3 phase 30ma RCD had been fried but the cable looked to be ok. Not being a 3 phase expert I pointed my friend at the faulty component which allowed him to call the right supplier.

But it's left me thinking - do the normal volts drop rules apply to delta configs?
 
as far as im aware normal volt drop applies, and using cablemate, i just did a cable calc, guessing 12A FLC, 25A type D, 5.5kw pump with power factor .8
came in at 10mm2 because of volt drop.

Sounds undersized for me, but ofcourse will need all details for a correct answer
 
Well it must be a dammed small motor to be wired in 2.5mm over a quarter of a mile!!

Motors generally require being wired with a cable that is sized, that will not drop voltage during it's starting/run-up time, when a higher current is flowing than it's normal FLC...
 
Came across a supply for a 3 phase delta water pump at a friends farm the other day, the cable appeared too small at 2.5mm swa given the distance (1/4 mile) so far as I was concerned. The 25A 3 phase 30ma RCD had been fried but the cable looked to be ok. Not being a 3 phase expert I pointed my friend at the faulty component which allowed him to call the right supplier.

But it's left me thinking - do the normal volts drop rules apply to delta configs?

Is this a pressurisation unit as opposed to a genuine water pump?
 
Yep ... that sounds about right!! Starting currents can be around 10x plus of FLC depending on motor configuration etc....
 
Thanks very much for the responses - I didn't go into the problem in too much detail as it was well out of my comfort zone, it is a pump, the head must be over 100ft so it must be fairly powerful. I assumed the installer knew what they were doing as it's all connected to a uv filtration unit and looks the part. Granted its not giving a massive flow or a high pressure, but it took out the 3 pole RCD and the 3 pole 16A MCB. I've been reading one or two threads about harmonics but ....? Anyway the thought at the mo is to fit a non-return valve to the intake and move the pump next to the UV filter. Stands a chance as long as the system can be primed.
 
Is the pump supplied by an inverter drive?

I don't know - didn't get that far with it - what should I be looking for - I assumed delta as only L1 L2 & L3 went to the control switch, the chasis was earthed and the neutral from the rcd went to the met, would this be the same in an inverter drive?
 
The volt drop needs to be such that it doesn't affect the operation of the connected equipment. If its the case that the pump will work safely at lower voltages then this way allow a larger volt drop to be utilized.
 
as far as im aware normal volt drop applies, and using cablemate, i just did a cable calc, guessing 12A FLC, 25A type D, 5.5kw pump with power factor .8
came in at 10mm2 because of volt drop.

Sounds undersized for me, but ofcourse will need all details for a correct answer

So there are other acceptable volt drop tables for 415V?
 
So there are other acceptable volt drop tables for 415V?

Normal voltage drop percentages do apply but as Chr!s has stated, the manufacturers tolerances are the limiting factor in these cases.
 
right - so if it were to be an inverter drive then harmonics may have distroyed the MCB & RCD as they could be overheating and the installer possibly should have installed cartridge fuses depending on manufacturers recommendations
 
Purely going on what the OP has told us,... ie cable size is 2.5mm, length of run around a quarter of a mile, a pump capable of rising water around a 100ft and through a UV filtration unit, and then onto wherever.

Now, i don't know about anyone else idea's here, but to my mind that cable is undersized for the size of motor it's supplying, and to say that motor has been struggling, ...is an understatement!!!
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Volts drop - 3 phase delta pump supply
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
20

Advert

Thread statistics

Created
leolec,
Last reply from
Knobhead,
Replies
20
Views
3,587

Advert

Back
Top