My go-to of choice:

View attachment 84139

Double pole, single module, no functional earth and no neutral flying lead!
17 RCBO's, surge protection, free tails gland kit, anyone want to hazard a guess as to cost price?
They only supply trade users.

£325?

That would be roughly the price of CP Fusebox board with 17x DP RCBOs, with SPD and tails kit.
 
With discount, £404.

Not a bad price when compared to most manufacturers and it'll be interesting to see how they progress in the market.

If some of these newcomers can prove their worth by continuing to turning out decent quality at a reasonable price, but maintaining backward compatability as technology progresses, there's no reason why they can't shake up the industry. I can't speak from experience, but it seems as though some big names aren't interested in the guy who fits their products or the consumer who finds parts aren't available when maintenance is required or upgrades are needed.

Fusebox seem to be grabbing a decent share of the domestic market and hopefully these guys can follow suit.
 
Not a bad price when compared to most manufacturers and it'll be interesting to see how they progress in the market.

If some of these newcomers can prove their worth by continuing to turning out decent quality at a reasonable price, but maintaining backward compatability as technology progresses, there's no reason why they can't shake up the industry. I can't speak from experience, but it seems as though some big names aren't interested in the guy who fits their products or the consumer who finds parts aren't available when maintenance is required or upgrades are needed.

Fusebox seem to be grabbing a decent share of the domestic market and hopefully these guys can follow suit.
SBS have been around for a while, changed ownership a couple of years or so back when David retired.
Been mentioned on this forum for over 6 years.
 
SBS have been around for a while, changed ownership a couple of years or so back when David retired.

My one concern about small scale production is its sustainability and the long term availability of replacement parts. Hopefully that wont be an issue.
 
As long as they don't put a permanent mark on the enclosure and units or they can be peeled off if they look similar, the mix and match police wont know if they fit well. ???
 
1) In order for an RCBO to comply with BS EN 61009, the RCBO does not have to have a separate (functional) earth connection. However, the standard specifies that an RCBO which has a separate earth connection must behave in a certain way to conform to the specification, but the separate earth connection is not mandatory. There are RCBOs currently available that do not have a separate earth connection, yet they achieve full compliance and conformity with the standard.
2) The functional earth is used as reference by the internal RCBO electronics to increase the sensitivity, speed of operation and allows the device to detect an earth fault even if the neutral becomes disconnected. Losing the neutral connection is rare event, especially in TN systems that are increasingly common today. The probability of losing the neutral and having an earth fault at the same time, a double fault condition, is statistically small and evaluated by some manufacturers as so small not be of significance when specifying protection devices. In spite of this, there are those who advocate fitting an RCBO with separate earth connection “just to be on the safe side”. The penalties for this theoretical risk are RCBOs with taller form factors and the extra connection which make consumer units and distribution boards cramped and harder to wire, pushing up required connection time and costs. Even worse some electricians don’t know how to terminate RCBOs and it is quite common to find RCBOs with the functional earth connections cut off, this is clearly bad practice for a device where the electronics relies on a earth reference for its sensitivity and speed of operation.
3) Most manufacturers of RCBOs with functional earth fly-leads insist that these leads must be disconnected during insulation testing to avoid damage to the sensitive electronics, and during earth impedance loop testing to avoid misleading results. A minority of manufacturers insist on the disconnection of the neutral fly-lead during testing in addition to the functional earth, it is therefore important to consult manufacturers instructions before testing. Removing and replacing connections adds to the time and cost of testing, however, there are other issues. First, there is the possibility of failing to reconnect the functional earth fly-lead, leaving the device operating under conditions other than those for which is was designed. Secondly, disconnecting fly-leads goes against one of the basic principles of installation testing, which is that the installation should be tested in the exactly the same state as it will be operated in service. However, we often break this aspiration in installation testing.


Hey, love the explanation. I am trying to apply it to a couple scenarios back here in Australia. When you mention the FE is in case the neutral were to disconnect. Which neutral are you referring to? Line side rcd circuit, load side of that circuit/rcd. Or the neutral tail that comes off the rcd?

From my understanding if any of these were to happen the circuit would be open and current wouldn’t flow. Or if there was still current and there was an earth fault. I am struggling by to work out how the rcd would differentiate which circuit has the earth fault Because all the FE from every rcd are together on an earth bar.

Thanks in advance, really appreciate it!
 
3) Most manufacturers of RCBOs with functional earth fly-leads insist that these leads must be disconnected during insulation testing to avoid damage to the sensitive electronics, and during earth impedance loop testing to avoid misleading results.
With some I've used from CPC in the past, they measure something like 65k L+N to E with one polarity, and near enough o/c the other way round.
My first test is the whole installation, using my old Megger (on 250V) so I can hold the button while any capacitance charges. With the MFT, it gives a false reading as it's still charging caps when it's finished the measurement. If that gives a decent reading, there's no point measuring individual circuits.

At 250V, no damage should occur.
Secondly, disconnecting fly-leads goes against one of the basic principles of installation testing, which is that the installation should be tested in the exactly the same state as it will be operated in service.
I work on the basis that the least you disturb the better. As you say, every connection you disturb is a potential fault introduced.
SBS have been around for a while, changed ownership a couple of years or so back when David retired.
Been mentioned on this forum for over 6 years.
Nice stuff, I belive it's LiVE stuff badged - the boxes are LiVE. The USP is (or was) the custom busbar to exactly suit your requirements - going back a bit, the MCBs were single pole and needed different tabs.
Unfortunately, I believe they've closed down
View: https://m.youtube.com/watch?v=FzA-EbrRVBE
 