Pictures


Any ideas? This is a picture the customer sent me so I aint had a propper look yet.

I need to put in a shower circuit and was going to split the tails (Henley block) and fit a shower consumer unit with 30ma rcd.

Could I put the shower unit after the RCD pictured.

Yes there is a spare way on the pic but this has now been used.
 

Attachments

  • cu.jpg
    29.4 KB · Views: 102
It should have the rating and hopefully a BS number on it and that would give some idea.

Is the install a TT? It may be the old VOLCB in which case, it needs renewing.

Only guessing mind.

If you are installing a shower then maybe the best way to go would be to do as you suggested, bearing in mind that you still need to make sure all earthing arrangements are satisfactory.
 
Replace with stand alone RCD in an enclosure, similar to whats fitted in the CU's nowadays.

Make sure the rating is sufficient for the load.

You can get them in 40, 63, 80amp etc, at 30mA.
 
3227898379
Pictures


Any ideas? This is a picture the customer sent me so I aint had a propper look yet.

I need to put in a shower circuit and was going to split the tails (Henley block) and fit a shower consumer unit with 30ma rcd.

Could I put the shower unit after the RCD pictured.

Yes there is a spare way on the pic but this has now been used.
can't make it out but it looks like a 4 module current operated rcd.If its 30ma and you wanted to provide descrimination you would be best taking your new rcd/shower unit supply from the line side of it.
 
I'd go with a board change, can't see alot of space for a shower CU in that cupboard! And if they wan't something else added in the future a 10way twin rcd board would make it easy!
 

Reply to What type of RCD is this? in the Australia area at ElectriciansForums.net

Similar Threads

i have faild napit annual assessment with silly mistake of using on consumer unit type AC rcd instead of Type A rcd. i bought type A rcd but they...
Replies
6
Views
690
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
733
Hello, I was looking at installing a SPD into an existing split load RCD BG consumer unit. In the instructions for the SPD it states that it may...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock