Was just watching a video of an RCBO install and found it weird that the breakers are double pole yet still have to have a fly lead.

Why don't we do it like this:

Ignore the gibberish coming out of his mouth and take a look at the unit. L+N coming from the supply, feeding the bottom of the first RCD. All the RCD's are linked together by the linking bars running down the left, giving them all L+N feed. The feed then goes through the RCD out the top, into the bus bar that's linked across the tops of all the MCB's. The L+N of each circuit comes out the bottom. This does away with the need for a neutral bar (there is one but they are used when there is no linking bar employed and you have to run an N to each RCD), several main neutral cables and the need to fill the unit with loads of extra cabling, not to mention cost saving on the materials.

Why, even with dual pole RCBO's, do we still make them use fly leads when we could simply link them all to N via the main RCD in? Makes no sense to me.

Having said that we're still the only country i know of that uses rings.

Anyone think we'll eventually catch up and stop doing things in such weird ways? Although i guess one drawback of the way they do it in Europe is that their multi tier units are standard for almost any regular sized home and they are anywhere from £3-700.
 
Like on this video, why don't they just have the N going through the bottom, then you could simply do L+N in the top of the RCD from the supply, L+N out the bottom of the RCD via bus bar into the bottom of the RCBO's then L+N out the tops for the circuits. That would do away with 10 extra N cables.

Or do these exist and i've just not seen them?

 
I agree 100% that there should be a neutral bus-bar so no abomination of flying leads.

Why does Europe have them already? Probably as they have often mandated DP MCBs due to a historical lack of a "strong correct polarity". The UK has had polarised plugs since well before WW2 and often only a switch or fuse in the line, as neutral was usually well--earthed (though you do occasionally see pre-WW2 cut-outs with a fused neutral - a bad thing these days). So when we had fuse or MCBs there was never a need for DP operation, so no neutrals going through them and no need for a neutral bus-bar.

That has changed with RCBOs, even though the majority of them in the UK are single-pole switching (I strongly believe in DP switching like the Wylex, Crabtree and Fusebox compact RCBO) it would be massively easier with a neutral bus-bar.

As for the RFC, arguments over it can be found here and it will run and run. But the key difference as to why the UK (and former commonwealth) has them and other don't is we have fused plugs and they don't. That massively changes the way you chose to rate the supply OCPD and manage the cable volt drop and rating. Also it means no single point of failure in the fixed wiring for the CPC (weakly with single terminal sockets, strongly if dual-terminal 'high integrity' sockets are used).
 
There are lots of historical influences on design of these things. @pc1966 mentions some of them, including the important factor that DP and SPSN MCBs became popular in Europe before RCBOs, because of wider use of TT.

We are used to being able to supply all the socket-outlets of a domestic installation with a small number of circuits, as each 32A circuit (whether ring or radial) offers 7.3kW. A small home will function perfectly well with just one 32A circuit; we would consider that bad design now but it was quite standard in the past. Using 16A circuits, more than two would be required to achieve the same level of utility since there is less diversity and any concentration of load can easily trip a 16A. Hence four or more circuits might be desirable to cover the same load and area, increasing the number of ways needed in the CU. This is all the more important in areas using supplies in the 110-127V range (which included parts of France until a few decades ago) which obviously only get half as much power per amp as those using the 220-250V range.

Some locations standardised on 3-phase for domestic supplies, with main fuses as low as 25A, leading to 3-phase cookers etc. with a corresponding increase in the number of outgoing ways. The result of these and other factors is that large multi-row CU's are fairly standard abroad, whereas we tended to stick to little boxes with as few as six outgoing ways even in the 1980s, bought as a complete thing and used as-is instead of being built as a system with a view to expansion.
 
There are lots of historical influences on design of these things. @pc1966 mentions some of them, including the important factor that DP and SPSN MCBs became popular in Europe before RCBOs, because of wider use of TT.

We are used to being able to supply all the socket-outlets of a domestic installation with a small number of circuits, as each 32A circuit (whether ring or radial) offers 7.3kW. A small home will function perfectly well with just one 32A circuit; we would consider that bad design now but it was quite standard in the past. Using 16A circuits, more than two would be required to achieve the same level of utility since there is less diversity and any concentration of load can easily trip a 16A. Hence four or more circuits might be desirable to cover the same load and area, increasing the number of ways needed in the CU. This is all the more important in areas using supplies in the 110-127V range (which included parts of France until a few decades ago) which obviously only get half as much power per amp as those using the 220-250V range.

Some locations standardised on 3-phase for domestic supplies, with main fuses as low as 25A, leading to 3-phase cookers etc. with a corresponding increase in the number of outgoing ways. The result of these and other factors is that large multi-row CU's are fairly standard abroad, whereas we tended to stick to little boxes with as few as six outgoing ways even in the 1980s, bought as a complete thing and used as-is instead of being built as a system with a view to expansion.
I always thought (coming from a French background) it prudent to do something like 2x radials on 20a MCB's + 32a ring for the kitchen, for a smaller house up to 100sqm.

Sound like something that is doable over here?

In France we basically use radials and then everything in the kitchen gets its own dedicated circuit, including washing machines and dishwashers.
 
my thinks......average house.RFC for kitchen, rest of sockets on 2/3 20A radials.
That's what i woulda thought - is it true that you're only allowed one radial per 50sqm area? I've heard this said but struggling to find the rule written down.

I thought RFC for the kitchen just because of the load being drawn if eg toaster, kettle, dishwasher and washing machine are all on at the same time.
 
That's what i woulda thought - is it true that you're only allowed one radial per 50sqm area? I've heard this said but struggling to find the rule written down.
There is no rule as such, just some guidance for "typical" usage. From memory it is 50m^2 for 20A radial, 75 for 32A radial and 100 for 32A RFC.

Recent tradition is one floor of a house would be on a RFC. More recently came the idea of one just for the kitchen as more power-hungry accessories came in to common use.

In truth the RFC is very robust, many place have everything on one and it is just fine. the more recent trend for more separate radial socket circuits in the UK is probably driven more by RCDs and accumulated leakage.

I thought RFC for the kitchen just because of the load being drawn if eg toaster, kettle, dishwasher and washing machine are all on at the same time.
I would agree. Some prefer 4mm radials but that is marginal if much thermal insulation, and by 6mm it is hard to wrnagle or fit pairs in to socket terminals..

But more often than not the main issue/guidance that seems relevant is separate single sockets per appliance, not doubles that seem to burn out more.

In Scotland the building regs say there must be accessible means of isolation for white goods, so you probably would have an RFC around 20A DP switches and each running 2.5mm to an unswitched socket behind the appliance, etc.
 
By the way, SBS make one....
I've been thinking about trying one when I find the right job for it.
Yes, they are nice boxes, and he's very flexible.
Also does some nice glands. The 25mm tail set he does fits in a 32mm hole, and there's an adapter if yo have a 40mm hole. The last one I got from the wholesaler (CEF) was 40mm an by the time you added an adapter down to 32mm it was a horrible monstrosity.
 
Yes, they are nice boxes, and he's very flexible.
Also does some nice glands. The 25mm tail set he does fits in a 32mm hole, and there's an adapter if yo have a 40mm hole. The last one I got from the wholesaler (CEF) was 40mm an by the time you added an adapter down to 32mm it was a horrible monstrosity.
CEF appear to do a 32mm one, though the image does not seem to match as it does for the 40mm one:
They also stock the Wylex one but at quite a price:
 
As I understand it, the double pole RCBO's only monitor the Phase side, the neutral side is just dragged along on a fault condition, so as you say it does break both.
 
Its all DP 2-mod rcbos here

Takes up more space ,.main boards are always at least ,2-row

Better job on an rcbo board to be breaking both live poles for a fault I reckon
You can get DP RCBOs in single width, like the compact Wylex, Crabtree, and fusebox RCBOs so they take no more space then traditional UK style MCBs.

I really prefer DP ones for various reasons:
  • They isolate both L & N so you can IR test the circuit without having to unscrew anything
  • If you have a TT style arrangement with an up-front delay RCD the you don't trip that on a N-E fault downstream (as N is isolated)
  • If you are really unfortunate and have reversed polarity, you still get some hope of a fault being interrupted (but you really don't want to test that out as the I2t of the relatively slow RCD opening action will be horrendous)
 
You can get DP RCBOs in single width, like the compact Wylex, Crabtree, and fusebox RCBOs so they take no more space then traditional UK style MCBs.

I really prefer DP ones for various reasons:
  • They isolate both L & N so you can IR test the circuit without having to unscrew anything
  • If you have a TT style arrangement with an up-front delay RCD the you don't trip that on a N-E fault downstream (as N is isolated)
  • If you are really unfortunate and have reversed polarity, you still get some hope of a fault being interrupted (but you really don't want to test that out as the I2t of the relatively slow RCD opening action will be horrendous)

Can you get a L+N busbar for the single width ?
 
You mean the MCB side of it ?
It'll be just on the L pole
?
It's one of those "you need to check" things. I expect the some of the two module types will sense (MCB function) on both poles, and some of the single module types don't even switch the neutral.
Some of the single module types sense on the L pole only (for the MCB function) but switch both poles. Obviously for the RCD function they sense on both poles.
 
Its all DP 2-mod rcbos here
The DP 2 mod rcbo, s with L and N busbar fed from underneath is undoubtedly one of the best designed and user friendly DB, s that's ever hit the market. It really should be the "gold standard". However, after 25 years of using them I, m sad to say, there appears to be a change on the way. (over here in ROI). Have you seen the latest Hagar designed DB based on the new 2021 regs?
 
The DP 2 mod rcbo, s with L and N busbar fed from underneath is undoubtedly one of the best designed and user friendly DB, s that's ever hit the market. It really should be the "gold standard". However, after 25 years of using them I, m sad to say, there appears to be a change on the way. (over here in ROI). Have you seen the latest Hagar designed DB based on the new 2021 regs?

No, I'm familiar with the changes to DBs in the new rules here, but haven't seen the Hager board
 

Attachments

  • IMG_20210830_111910.jpg
    IMG_20210830_111910.jpg
    558 KB · Views: 73
  • IMG_20210830_111841.jpg
    IMG_20210830_111841.jpg
    474.8 KB · Views: 73
The DP 2 mod rcbo, s with L and N busbar fed from underneath is undoubtedly one of the best designed and user friendly DB, s that's ever hit the market. It really should be the "gold standard". However, after 25 years of using them I, m sad to say, there appears to be a change on the way. (over here in ROI). Have you seen the latest Hagar designed DB based on the new 2021 regs?
What's actually in the Hager board

We're very similar to the UK now non-, combustible boards, arc fault and surge protection

Heading towards all rcbo although I think it's only a recommendation

They can't seem to think straight on bathroom lighting ,went ott with emergency lighting and rcbos and now they're allowing it on a shared rcd if I'm not mistaken
 
I install this tomorrow. First rewire under new regs. To my great surprise the single module rcbo and the "dreaded flylead" has invaded our shores. Our beloved 2 pole rcbo and L +N busbar is being sacrificed for space in preparation for rcbo populated DB, s.
 

Thanks I forgot the DP main isolation about time there , more harmonization with the UK

Surge protection

Dual RCDs is it , so that would be base spec in comparison to an rcbo board. ?

Didnt take a proper look yet but if they're gone from lighting mcbs to lighting on shared RCDs that would be a backward step
 
And that's a shower rcbo too

I do shoot from the hip

Nice board

Good to see the DP main isolation and lighting rcbo kept separate from power , if its even advisable for domestic lighting in the first place which I have my doubts
 
I install this tomorrow. First rewire under new regs. To my great surprise the single module rcbo and the "dreaded flylead" has invaded our shores. Our beloved 2 pole rcbo and L +N busbar is being sacrificed for space in preparation for rcbo populated DB, s.

Hate to break this to you, but those shores were breached some time back - now we're just slipping them over the border ?

On a more serious note, if single module RCBOs are going to become more commom in IE, it might be an idea to look at options that don't require a flylead - at least until such times as Hagar catch up.
 
Thanks I forgot the DP main isolation about time there , more harmonization with the UK
What is very different though is the use of a 63A B-curve MCB as input isolator.

Certainly I think isolation should always be all-pole (though for TPN that is not so common and ideally then you want a mate first / break last on N) and I was surprised that ROI did not do so in the past.

The use of the MCB to me is kind of mixed, I can see it is a good idea to limit each CU's total current without pushing the DNO fuse in to that job (I presume ROI still has the equivalent of a fuse as ultimate limiter?) but it also seems a bad idea on selectivity as many high current faults will take out both the faulty circuit and the whole damned supply!

63A B-curve instant trip is 189-315A, though looking at the Hager tables it would be selective with a 20A B-curve for socket radial to around 700A. That is still less than often seen for PSSC on sockets here (my experience mostly the RFC, maybe easier at ends of 20A radial though?).
 
What is very different though is the use of a 63A B-curve MCB as input isolator.

Certainly I think isolation should always be all-pole (though for TPN that is not so common and ideally then you want a mate first / break last on N) and I was surprised that ROI did not do so in the past.

The use of the MCB to me is kind of mixed, I can see it is a good idea to limit each CU's total current without pushing the DNO fuse in to that job (I presume ROI still has the equivalent of a fuse as ultimate limiter?) but it also seems a bad idea on selectivity as many high current faults will take out both the faulty circuit and the whole damned supply!

63A B-curve instant trip is 189-315A, though looking at the Hager tables it would be selective with a 20A B-curve for socket radial to around 700A. That is still less than often seen for PSSC on sockets here (my experience mostly the RFC, maybe easier at ends of 20A radial though?).
Yes. There has always been a switch fuse between the DNO and the customers DB. A short circuit on the cooker or shower circuit could potentially take the 63 amp mcb out but to date I have not experienced it. All installations are entitled to install a 63 amp "C" curve if the Fli allows for it which most will.
The DB on the picture is not available off the shelf yet in most wholesalers and I was, nt given a choice. I had to order direct from Hagar as I have a job to finish. Still struggling to get the new LZSH in all the necessary sizes due to the delays caused by covid
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
Why do we do it the way we do in the UK?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
74
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
Electrics,
Last reply from
LastManOnline,
Replies
74
Views
9,139

Advert

Back
Top