There could be a shared neutral on the ring, such as if the boiler was separately supplied and then someone partially moved it on to the ring, say just to get a line supply.
Or there could be a mixed up neutral on another circuit but there was not enough leakage to cause the RCD to trip until the load of the ring was placed on that RCD.
 
Plasterer mate of mine got a belt of a wall turns out there used to be wall lights, yep you guessed it still live taped up and squashed into a hole
P
 
Had an rcd tripping yesterday when one side of a double socket was switched on, regardless of anything being plugged in.

Had left about an hour earlier after doing an eicr so I knew the rcd was fine, quickly worked out it was the kitchen and that one socket, kettle had been plugged in and it went. Put new socket and it held, was obviously something it didn't like after I'd fiddled about with it first time round.

As for the OP, have you checked outside the kitchen as well for anything spurred off the circuit?
 