Be careful how you word this, you may know what you mean here but OP isn't an electrician. Loss of a phase through a three phase mcb alone will not cause it to trip whether from the supply side or broken wire load side, having said that and as you noted in previous post it may cause excessive current rise in other phases and this will depend on the load and its characteristics i.e. if a 3ph motor connected then it will 2phase on start-up giving high current spike on the stalled motor until it is detected by the motor overload or mcb or if poorly designed install/control circuit then until the motor catches fire and shorts
Oga does your breaker have overload function or capacity. If yes then single phasing automatically gives more load to the remaining 2 phase which depending on the breaker's rating as against the load can either trip or withstand the load. Hence, on installation every breaker rating should be a little more than the load that is given to it.
 
Oga does your breaker have overload function or capacity. If yes then single phasing automatically gives more load to the remaining 2 phase which depending on the breaker's rating as against the load can either trip or withstand the load. Hence, on installation every breaker rating should be a little more than the load that is given to it.
This thread is 8 yrs old, I can confidently say it has been resolved imho, please cheque the time stamps on thread/posts before responding. :)
 

Reply to Will 2 out of 3 Phases Trip a 3 Phase Breaker? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a question hoping I can get some help. I wanted to know if there is a 400V 3 phase supply (A/A/A) terminated on the primary side of a...
Replies
3
Views
853
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
828
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
567
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
847
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock