Using a fused 80A switch at origin to protrect SWA running to consumer unit on upstairs flat.

I've wired it so that the meter tails enter at the top of the double pole isolator i.e the tails running to the meter are fused rather than the supply to the consumer unit.

The meter installation guy has insisted that they be swappwed round saying that the meter tails must enter the switch and the SWA line is what should go into the fuse-holder. As it turns out not a problem but as far as I can see both solutions provide a double pole isolator between meter and consumer unit and overload protection so what's the deal?
 
Because the double pole switch should isolate the supply not the fuse which is basically single pole.
when you pull the fuse you should isolate first via double pole switch
 
Using a fused 80A switch at origin to protrect SWA running to consumer unit on upstairs flat.

I've wired it so that the meter tails enter at the top of the double pole isolator i.e the tails running to the meter are fused rather than the supply to the consumer unit.

The meter installation guy has insisted that they be swappwed round saying that the meter tails must enter the switch and the SWA line is what should go into the fuse-holder. As it turns out not a problem but as far as I can see both solutions provide a double pole isolator between meter and consumer unit and overload protection so what's the deal?

You do not own the tails from the head to the meter, they are the property of the DNO. The tails FROM the meter are yours. If you need to provide an isolator on your supply this must LEGALLY be upstream of the meter because you are not legally allowed to interfere with the DNO services, you risk being charged with a criminal offence.
 
You do not own the tails from the head to the meter, they are the property of the DNO. The tails FROM the meter are yours. If you need to provide an isolator on your supply this must LEGALLY be upstream of the meter because you are not legally allowed to interfere with the DNO services, you risk being charged with a criminal offence.

Are you sure?
 
Are you sure?


Yup, only the DNO is allowed to put an isolator between the head and a meter. The exception would be were the head feeds a DNO master meter and this then feeds a DB or split services to sub meters, then you could install an isolator between the master meter and the sub meters. It's all laid out in the Electricity Safety, Quality and Continuity Regulations 2002 and the ACOPs that the DNO's all have to abide by.
 
Yup, only the DNO is allowed to put an isolator between the head and a meter. The exception would be were the head feeds a DNO master meter and this then feeds a DB or split services to sub meters, then you could install an isolator between the master meter and the sub meters. It's all laid out in the Electricity Safety, Quality and Continuity Regulations 2002 and the ACOPs that the DNO's all have to abide by.

I agree .... what confuses me is what you're calling upstream of the meter. ............ Be gentle - I'm just a thick old Geordie. ;)
 

Reply to Wiring meter tails into switched fuse? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
426
Just wanted to know which people use. My case. Client converting attached garage into new rooms. Consumer Unit has to move to accomodate this...
Replies
7
Views
1K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
809
Hi we have been asked to run a 3 phase supply into a boiler house to feed a DB fed from next to the existing meter. Would we need to install Tails...
Replies
2
Views
804
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
968

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock