Using a fused 80A switch at origin to protrect SWA running to consumer unit on upstairs flat.

I've wired it so that the meter tails enter at the top of the double pole isolator i.e the tails running to the meter are fused rather than the supply to the consumer unit.

The meter installation guy has insisted that they be swappwed round saying that the meter tails must enter the switch and the SWA line is what should go into the fuse-holder. As it turns out not a problem but as far as I can see both solutions provide a double pole isolator between meter and consumer unit and overload protection so what's the deal?
 
Because the double pole switch should isolate the supply not the fuse which is basically single pole.
when you pull the fuse you should isolate first via double pole switch
 
Using a fused 80A switch at origin to protrect SWA running to consumer unit on upstairs flat.

I've wired it so that the meter tails enter at the top of the double pole isolator i.e the tails running to the meter are fused rather than the supply to the consumer unit.

The meter installation guy has insisted that they be swappwed round saying that the meter tails must enter the switch and the SWA line is what should go into the fuse-holder. As it turns out not a problem but as far as I can see both solutions provide a double pole isolator between meter and consumer unit and overload protection so what's the deal?

You do not own the tails from the head to the meter, they are the property of the DNO. The tails FROM the meter are yours. If you need to provide an isolator on your supply this must LEGALLY be upstream of the meter because you are not legally allowed to interfere with the DNO services, you risk being charged with a criminal offence.
 
You do not own the tails from the head to the meter, they are the property of the DNO. The tails FROM the meter are yours. If you need to provide an isolator on your supply this must LEGALLY be upstream of the meter because you are not legally allowed to interfere with the DNO services, you risk being charged with a criminal offence.

Are you sure?
 
Are you sure?


Yup, only the DNO is allowed to put an isolator between the head and a meter. The exception would be were the head feeds a DNO master meter and this then feeds a DB or split services to sub meters, then you could install an isolator between the master meter and the sub meters. It's all laid out in the Electricity Safety, Quality and Continuity Regulations 2002 and the ACOPs that the DNO's all have to abide by.
 
Yup, only the DNO is allowed to put an isolator between the head and a meter. The exception would be were the head feeds a DNO master meter and this then feeds a DB or split services to sub meters, then you could install an isolator between the master meter and the sub meters. It's all laid out in the Electricity Safety, Quality and Continuity Regulations 2002 and the ACOPs that the DNO's all have to abide by.

I agree .... what confuses me is what you're calling upstream of the meter. ............ Be gentle - I'm just a thick old Geordie. ;)
 
Except..... (and I've said this before, so apologies for the parrot)...I've had guys from WPD say that they won't fit an iso downstream of the meter due to it technically falling under part P, and the DNO's aren't Part P registered!
 
Except..... (and I've said this before, so apologies for the parrot)...I've had guys from WPD say that they won't fit an iso downstream of the meter due to it technically falling under part P, and the DNO's aren't Part P registered!

They have a point.

The issue I'm having with this thread is the confusion / controversy over which way is upstream and which is downstream.

Me - being a simple Geordie - relates everything to the River Tyne. (It was a Big River ye knaa)

The River Tyne starts up a height in the hills and runs down to meet the North Sea at Tynemouth, so my simple Geordie logic tell me that the source of the river is UP stream and where it ends- up is DOWN stream.

To relate this to the electrickery, UP stream is the big building stuffed full of Babcock & Willcox boilers and Charlie Parsons steam turbines and DOWN stream is the 40 Watt bulb (sorry .. LAMP) hanging from the ceiling in me Granny's netty at the bottom of the back yard.

Have I understood this correctly?
 
Me - being a simple Geordie - relates everything to the River Tyne. (It was a Big River ye knaa)

The River Tyne starts up a height in the hills and runs down to meet the North Sea at Tynemouth,
Divvent fogit Sooth Shiels man, thas mair than one pier ye knaa :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Wiring meter tails into switched fuse?
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
31

Advert

Thread statistics

Created
RubberGrommet,
Last reply from
Outspoken,
Replies
31
Views
7,578

Advert

Back
Top