I would also be using flexible conduit (contractor pack) with p clips for some protection also mate..
Quote" original post
Apart from the obvious ie, max demands and bonding requirements have I missed anything, and is the cable I intend to use ok. Unquote"
But your comment is appreciated itselectric and a valid and useful one. Of course bonding of extraneous conductive parts, including the chassis will be completed.
Looks like my choice of cable is ok. As Glennspark as pointed out ref 6
Thanks mate.
your welcome Bald.:wink:
OK Baldy, I've decided to play nice :D
Working on mobile units can be a bit of a minefield if you're not exactly sure what you're doing. I must say that I am no 'expert' but I have worked on them before. You sound like you are planning on finding hardwired supplies from wherever you take the trailer, if this is the case then there are a few things you need to take account of, the first one being.... The fixed supply plug on your trailer needs to be male, to be able to accept a female socket on to it.
Secondly, you need to be able to make sure that the trailer is never used as part of a TN-C-S system unless directly under your supervision. This can realisticly be achieved in one of two ways; 1. relying on a rod and an RCD whenever you're plugged into a permanent supply (making your trailer a TT system), or 2. relying on electrical separation as your protective measure for if you're plugged into a generator. This method is by far the safest method of protection and I would choose this over ADS any day of the week!
The way to set this up is ultimately to wire as you normally would any installation with an RCD as your main switch, preferrably a 10mA, and making sure that all exposed conductive parts within the trailer are supplementary bonded to themselves and to the chassis (remember that this is not an extraneous conductive part). The other thing worth noting is that you will not have an earthing conductor to your fixed supply plug as you will either be relying on an earth rod or on no earth reference at all. At no point will you want to be picking up an earth from the supply unless you can be absolutely sure that every single supply you tap into is TN-S.
If wiring into a permanent supply you'll obviously have to bang a rod in (wired from your main earthing terminal) every time you park up and do business. This will have to be tested on every occasion you do so and you will go through a few rods! lol. If plugging into a genny then you will be relying on electrical separation and therefore you want nothing earthed (no rod!), only bonded to each other, which is effectively what your cpcs now become in each circuit. Bear in mind that your RCD is now useless when relying on a generator with no tapped earth. An ideal wiring system would be stranded cable to BS 7211 (I think) wired within plastic flexible conduit throughout the trailer. This is so you can get a 2.5mm cpc to every accessory to keep your ohmic readings between accessories negligable.
With regards to your supply, you really do want to be accurate about your demand. If you have a socket circuit which will only pull 2.5A then put it on a 3A MCB, if your lights will only pull 0.5A put them on a 1A MCB. The last thing you want is an installation on an unprotected 16A supply but with the potential to pull 38A (16A + 16A + 6A) if other stuff unrelated to you is plugged in.
I fear I am now rambling, my excuse is that I've had a few beers so feel free to shoot me down if I've left something out that I should have put in or put something in that I should have left out.
Exactly the opposite regarding the male commando. Think about it !!
Flex for caravans and trailers due to vibration ect.
And its a mobile unit so hookup could be any 16A supply where ever they are.
Be nice guys, (Give him enough rope to hang himself) That's not a tradesman talking, but we know the type, there's always one. lol.
Ah completely missed "mobile"!
My friend has two coffee trailers, I did not carryout the electrical installation, however I have been and carried out periodic inspections on them on two occasions. Everything is bonded, but it is for the most part wired in twin and earth in plastic conduit. Generally they are powered by Honda smart generators (2 of) that can be linked to increase capacity if needed. There is an RCD main switch installed that becomes entirely non functional when power is supplied from the generators. But comes into effect as soon as the trailers are plugged in at his home. In this case is an earth rod really required? I actually installed one temporarily and it appeared to make no difference to the correct operation of the RCD (including the one feeding his garage, feeding the socket outlet) which both tripped quickly.
Any thoughts on this?
His house would have been a TN-S and the supply would have had an earth core in it.
As someone who has worked on event sites and provided power to umpteen caterers I would recommend a 32A input as the amount of vans I visit where they have two 13A tea urns and a small water heater boiling away on a 16A input and wonder why the power has gone off... where only a 16A supply is available through in a 16A to 32A jumper - should cost £15 and can be carried round.
There was one fish and chip van in Hyde Park last year that turned up with a 63A three phase input (which tripped a few times due to overload)!
Any cabling supplied for connecting up to the unit should be rubber flex as anything external is covered by BS7909 which prohibits Arctic for outside use
You'd get away with 16A for only a couple of sockets, a few lights and a small BV if your burners are running on gas, but yeah, you're absolutely right, 32A would be better!
I have seen many occasions where caravans have plugged into 16A 30ma rcd supplies usually
TN-S as you have pointed out.
From what you say, the user of a portable unit should identify the means of earthing and suitability, and also consider the use of a rod where appropriate.
In the real world I wonder how many take those measures.
Can you make such an installation for portable vans and trailers idiot proof by design ??
Probably not, but how far can you or how far do caravan manufacturers and the like go ???
Thanks for post 18 sir.
whatever you do with this damn burger bar do it quickly , there'll be truckers on the A6 wanting their breaky in the morning.
Barely anyone lol!
To a certain degree yes, make sure the installation comes with a genny and tell them NEVER to tap into a permanent supply. Maybe modify the genny and trailer so that they have a totally proprietary plug/socket system??
I've got a mobile library to test in the near future. 230v genny on board supplying sockets for computer points. I haven't seen it yet, so don't know too much about it. The firm involved build special vehicles but this is a bit unusual for them, I think. Looks like electrical separation will be needed..... I feel a little more than they expect.