I carried out a EICR and the main switch for the consumer unit is only rated at 60 amps and the main supply fuse is a BS1361 rated at 100 amps.

Im thinking this should be a C2, what are your thoughts please.

Many thanks

Martin
 
How do you know it's 100 amps , very rare to get a domestic fuse at that rating normally 60 or 80 amps
 
I carried out a EICR and the main switch for the consumer unit is only rated at 60 amps and the main supply fuse is a BS1361 rated at 100 amps.

Im thinking this should be a C2, what are your thoughts please.

Many thanks

Martin

What is the potential danger you have identified?
 
I was thinking the potential danger is the switching capacity isn't high enough in case of a fault.

That's not a danger, that is a fact about the inadequacy of the equipment.
What situation can you imagine where the main switch will be required to break fault current?
What is the total load on the board? Is it a fixed load or variable?
 
Haven't changed this board. I want to change it but need to discuss it with the owner but he doesn't like spending money.

You want to change it? I hope that is just a lapse of concentration and not a serious comment!
 
That's not a danger, that is a fact about the inadequacy of the equipment.
What situation can you imagine where the main switch will be required to break fault current?
What is the total load on the board? Is it a fixed load or variable?

There a four 3kw storage heaters on this board. So a load of 52 amps been drawn.

So the load is under the 60 amp rating of the main switch.
 
you can't do anything till you've assessed the load on this CU. get the clamp meter out at midnight.
 
There are thousands of cu's out there with 60 amp dp switches backed by 100amp service fuse.

That doesn't necessarily make it right though. There are thousands of 3036 CUs with a bit of 2.5 in place of the fusewire too.
 