Hi All i know its late friday, but try and help me out with this one if you can.
Just got in now from work on the way home a landlord called me to ask if i could test a communal DB he has at an HMO.
I decided to have a look on the way home, long story short each flat was feed from this DB including the communal circuits(lights,sockets).
so i checked Zdb to each flat which was ok but when i did R1+R2 test on the supply cable to each flat i got nothing,tried to each flat and 4 out of the 5 came back with a zero reading.
Distribution board was contactum,each flat was feed from a 40 amp b type mcb (No RCD on DB).

Any thoughts as its got me wondering, the Zdb to each flat was ok but R1+R2 no reading at all.
 
each flat had a 10mm t+e feed from the distribution board,and yes i am sure i was testing each distribution circuit with the L+E linked out,
 
i am taking my readings from phase and earth to each flat from the main distribution board is dead with the earth and phase linked out.
i thought it might be my tester (fluke 1653)but i checked my own house when i got back tested fine,double checked the cal quickly witb my cal card.all ok.i have zs and ze for the installation,i will post those tomorrow as i am out at the inlaws at the moment so i will post it in the morning.
 
Even if hes testing with main earth and bonding connected, then removing them ain't going to make an R1 R2 figure appear.

Must be testing wrong, if submains are T and E then can't see how R2 can be lost
 
Last edited:
i agree with your post but i am positive i am testing it correctly,as i said in my original post,4 out of the 5 came back open circuit,but 1 which was the top floor flat tested ok R1+R2.
thanks for your input fellas i will try R2 method on monday and report back
 
Even if hes testing with main earth and bonding connected, then removing them ain't going to make an R1 R2 figure appear.

Must be testing wrong, if submains are T and E then can't see how R2 can be lost

But if he,s getting a Zdb reading he could be getting yhis through parrell paths of the bonding. When in actual fact he's got no earth. :thumbdown:

Sent from my GT-I9100 using Tapatalk
 
By any chance have you switched each mcb off and linked from the output of one mcb to the earth bar on the CU this would give you the readings you describe?
 
Hi All i know its late friday, but try and help me out with this one if you can.
Just got in now from work on the way home a landlord called me to ask if i could test a communal DB he has at an HMO.
I decided to have a look on the way home, long story short each flat was feed from this DB including the communal circuits(lights,sockets).
so i checked Zdb to each flat which was ok but when i did R1+R2 test on the supply cable to each flat i got nothing,tried to each flat and 4 out of the 5 came back with a zero reading.
Distribution board was contactum,each flat was feed from a 40 amp b type mcb (No RCD on DB).

Any thoughts as its got me wondering, the Zdb to each flat was ok but R1+R2 no reading at all.

Alright Delboy :D

Interesting thread btw.

Having re-read your opening post, I can only surmise that R2 for the sub main is broken for 4 of the 5 flats. As others have pointed out you may very well still get a cracking Zdb via parallel paths (spesh if Bonding in place for water service in each flat for example and this runs via pipework back to DB1 - the origin board so-to-speak).

So Mr R2 test will reveal all. Hopefully.
 
Are you sure the circuits are labeled correctly???

i.e you linked r1+r2 at DB circuit labeled flat1, testing at flat 1 but the r1+r2 circuit is actually flat 4?
 

Reply to Zdb ok but no R1 + R2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock