Discuss Zdb ok but no R1 + R2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Delboy10
Hi All i know its late friday, but try and help me out with this one if you can.
Just got in now from work on the way home a landlord called me to ask if i could test a communal DB he has at an HMO.
I decided to have a look on the way home, long story short each flat was feed from this DB including the communal circuits(lights,sockets).
so i checked Zdb to each flat which was ok but when i did R1+R2 test on the supply cable to each flat i got nothing,tried to each flat and 4 out of the 5 came back with a zero reading.
Distribution board was contactum,each flat was feed from a 40 amp b type mcb (No RCD on DB).
Any thoughts as its got me wondering, the Zdb to each flat was ok but R1+R2 no reading at all.
each flat had a 10mm t+e feed from the distribution board,and yes i am sure i was testing each distribution circuit with the L+E linked out,
i am taking my readings from phase and earth to each flat from the main distribution board is dead with the earth and phase linked out.
i thought it might be my tester (fluke 1653)but i checked my own house when i got back tested fine,double checked the cal quickly witb my cal card.all ok.i have zs and ze for the installation,i will post those tomorrow as i am out at the inlaws at the moment so i will post it in the morning.
Even if hes testing with main earth and bonding connected, then removing them ain't going to make an R1 R2 figure appear.
Must be testing wrong, if submains are T and E then can't see how R2 can be lost
i agree with your post but i am positive i am testing it correctly,as i said in my original post,4 out of the 5 came back open circuit,but 1 which was the top floor flat tested ok R1+R2.
thanks for your input fellas i will try R2 method on monday and report back
But if he,s getting a Zdb reading he could be getting yhis through parrell paths of the bonding. When in actual fact he's got no earth. :thumbdown:
Sent from my GT-I9100 using Tapatalk
By any chance have you switched each mcb off and linked from the output of one mcb to the earth bar on the CU this would give you the readings you describe?
Alright Delboy :D
Interesting thread btw.
Having re-read your opening post, I can only surmise that R2 for the sub main is broken for 4 of the 5 flats. As others have pointed out you may very well still get a cracking Zdb via parallel paths (spesh if Bonding in place for water service in each flat for example and this runs via pipework back to DB1 - the origin board so-to-speak).
So Mr R2 test will reveal all. Hopefully.
Are you sure the circuits are labeled correctly???
i.e you linked r1+r2 at DB circuit labeled flat1, testing at flat 1 but the r1+r2 circuit is actually flat 4?
I have returned to the thread chaps sorry about the long time away,I should have updated this ages ago apologies all round.
Right long story short went back a few days later, long wandering extension lead in hand, found out it was exactly what VMAN suggested the D.B was incorrectly labelled apart from flat 5, so when I thought I was doing r1+r2 on flat 1 it was actually flat 3 as labelled on the board.
thanks to everyone who posted for your help and suggestions
nice on lads
(don't worry in future I will report back straight away)
Reply to Zdb ok but no R1 + R2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
hi all just got a Q regarding how to find R1 then second Q how to find R2 what i did so far was mutiplying each answer for1.67 so I could get the...
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Got my am2 coming up on Tuesday and I know I have to calculate my Zs readings Maybe I’m overthinking this but am not sure if I need to use the Ze...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...