Were there any suspicious IR readings? Particularly in the N-E department?



The question was no how many leads did you connect, but whether it is a two or three lead test? These are different things!

Ditto IR fault (neutral-earth), can cause RCD to trip on Zs 3 lead test.
 
Ditto IR fault (neutral-earth), can cause RCD to trip on Zs 3 lead test.

Exactly, and you'd hope that anyone who is carrying out these tests would actually understand what they are testing and the basic principle of how the tester performs the test.

I don't understand the mindset of just pushing the test button and writing the number down, what does it really achieve?
 
Try clamping the tails to see what leakage is there before you test as even on No Trip your still injecting 15mA into the cct so you may have a leakage which puts the RCD above its Ramp value just a thought!

Odd, I thought the megger used 200mA with DC blocking on the low current test?
 
Definately no trip guys.
Megger 1730. Two settings hi and low and I'm on low
Yes tried it on next doors circuits. Worked fine. It's the first time it's tripped rcd on a zs test with me.

My 1730 has three loop impedance functions on the L-PE setting:

3Lo (3 wire non tripping loop for RCD protective circuits (Zs))
2Hi (2 wire high current loop measurements (Ze/PFC))
2Lo (2 wire non tripping loop for RCD protective circuits (Zs)
 
Exactly, and you'd hope that anyone who is carrying out these tests would actually understand what they are testing and the basic principle of how the tester performs the test.

I don't understand the mindset of just pushing the test button and writing the number down, what does it really achieve?

Well I have to plead guilty there, but when something doesn't function as it should, there's always a reason. And in this case, I suspect the neutral-earth fault, somewhere.
 
You'll know better than me, my manual for Loop Tests says, test current 4.0 A (at 230v) on Hi, and Pulsed on Lo (Megger 1730).

Not necessarily, I've only had the megger a few months and don't get much use out of it so am not so familiar with it as I should be.

The pulsed current I guess would be the 2 wire no trip?
 
Pulsed current for 3 wire low & 2 wire low.

Yeah I just read the manual, interesting.

I also noted how the manual talks about the possibility of RCD tripping even on low current tests, the possible cause and that an alternative method may need to be used.
I guess the OP didn't bother to read the manual for his tester!
 
Your a bit harsh davesparks, most blokes get their new playstation out and connected it up. When it doesn't work, only then will they read the instructions. Still learning now with my MFT.

Never had a prob tripping RCD's on the low test currents, other than when I installed a luminaire for a customer and did a Zs test, for old times' sakes, and tripped the RCD. It was only going back to basics, did I find a neutral-earth fault on the circuit, re hum dinger!
 
Well I have to plead guilty there, but when something doesn't function as it should, there's always a reason. And in this case, I suspect the neutral-earth fault, somewhere.

Exactly what I think. But it definately is not internal.
 