hi guys,
Hoping for a little advice.
Been working on a property this week and have been having trouble getting zs readings as it trips the rcd on a 17th edition cu.
Property is pme. I've tried testing idividual circuits one by one and completely disconnecting all the others but it still trips. It doesn't seem to matter what circuit is tested it trips on every one.
I've checked absolutely everything and all tests leading up are fine. Zs tests however trip rcd.
I've done a ramp test on rcd to check that and it's fine.
I've got a feeling it's a Dno issue but they have now confirmed there are no faults on the line. Anyone had similar issues.
Thanks in advance
oops uploaded 3 times...... daaaaaan?
I'm with tel, if it's happening on every circuit it sounds like you're running a standard Zs test rather than a no-trip.
Also, make/model dependent, make sure you are using 3-leads if your tester requires it. When I first got my tester, I was running a no-trip Zs, but only with 2 leads having been used to a Megger. Turns out my Metrel needs 3 leads to do the no-trip.
the 1552/3 meggers use 3 leads. it's only the 1700 series that can do no trip with 2 leads.
Definately no trip guys.
Megger 1730. Two settings hi and low and I'm on low
Yes tried it on next doors circuits. Worked fine. It's the first time it's tripped rcd on a zs test with me.
on testing zs on the megger 1730, it is possible you have a problem tester I self.
when testing 3 low using plug or leads their should not have a problem
I had same problem many years back with 1502 sent it back megger sent me a new one .
did you turn the dial to off position and start again.
Were there any suspicious IR readings? Particularly in the N-E department?
Plug with three leads and two leads on lighting circuit. Doesn't matter what combination still trips
The question was no how many leads did you connect, but whether it is a two or three lead test? These are different things!
Try clamping the tails to see what leakage is there before you test as even on No Trip your still injecting 15mA into the cct so you may have a leakage which puts the RCD above its Ramp value just a thought!