How have you confirmed that it is not internal?Exactly what I think. But it definately is not internal.
Have you tested with the alternative Zs method?
How have you confirmed that it is not internal?Exactly what I think. But it definately is not internal.
How have you confirmed that it is not internal?
Have you tested with the alternative Zs method?
Not yet Dave I'm there tomorrow and will keep you posted
Back to the OP - given its a 17th Ed CU, what does your tester do with the 2nd RCD?
It is a 17th ed cu and if I'm testing a circuit covered by that rcd it still trips. Doesn't matter which circuit covered by rcd 1 or 2 it still trips.
Yeah I just read the manual, interesting.
I also noted how the manual talks about the possibility of RCD tripping even on low current tests, the possible cause and that an alternative method may need to be used.
I guess the OP didn't bother to read the manual for his tester!
That answer does not make sense!
Are you saying BOTH RCD's trip?
Have you tested your tester on another RCD?
Thing is Dave it's never happened before and I've tested many circuits/properties. Why now???? Why the 2 rcds????
Thanks Tony at last some decent advice. Thank youTry clamping the tails to see what leakage is there before you test as even on No Trip your still injecting 15mA into the cct so you may have a leakage which puts the RCD above its Ramp value just a thought!
It doesn't trip the 2 rcds. It trips the rcd to which that circuit I'm testin is covered by. Make sense??
My meter does not give me the option of 3 lead test or 2 lead lest although it will carry out the test with two leads.
P-le on low or hi
And p-n on hi only.
Well if you read what I wrote it obviously stays on.Let me rephrase the question.
What happens when you test the "other" RCD!
I have. It does not give me options of a 3 lead test or two lead test.I thought you said you had a Megger 1730?