Someones told me that to comply with the latest regs then a split load board with half the circuits as rcbos & the rest on mcbs with an RCD is no good & all rcbos is the way to go.
I can see the point but it seems overkill ???
 
Someones told me that to comply with the latest regs then a split load board with half the circuits as rcbos & the rest on mcbs with an RCD is no good & all rcbos is the way to go.
I can see the point but it seems overkill ???
Someone has been telling you porkies mate
 
Not that I am aware of, I'll take a look but it's a new one on me. But yes a board full of RCBOs is ultimately better.
 
Someones told me that to comply with the latest regs then a split load board with half the circuits as rcbos & the rest on mcbs with an RCD is no good & all rcbos is the way to go.
I can see the point but it seems overkill ???

Dual RCD CU complies with 17th full stop. Anything with RCBO's which will reduce disruption to rest of install under single circuit earth fault condition is going to be better but certainly not a requirement.
 
His idea was that no interaction between circuits is allowed & one circuit tripping the RCD and taking out several others is interaction.
Thanks for the replies ... I'm not totally up to speed with things & I'm thankful of that input..
 
His idea was that no interaction between circuits is allowed & one circuit tripping the RCD and taking out several others is interaction.
Thanks for the replies ... I'm not totally up to speed with things & I'm thankful of that input..

He is right in what he is saying. However it is not a requirement. Ask him to quote regulation that stipulates RCBO's.
 
The Regulation that refers to this is: "314.2 Separate circuits shall be provided for parts of the installation which need to be separately controlled, in such a way that those circuits are not affected by the failure of other circuits, and due account shall be taken of the consequences of the operation of any single protective device."
 