Hi,

As per title, how would you feel about connecting a few garage lights onto some 0.75mm flex straight into the 6A MCB, ignore switching, just that its 0.75mm.

I have to say I normally go via a FCU but in this occasion I don't feel I need to as its in the garage with a 6A MCB I can come off.

referring to table 4F3A on page 378 it states 0.75 can take 6A.

id say I'm good to go, I k ow I'm probably stating the obvious but it's not something I usually do, hooking such a small co doctor up to an MCB.

reason for it being small is due to the fact I'm using 3 core and earth flex so I can use the switched output on the lights so they Interconnect on PIR.
 
So with reference to my post #8, Am I wrong in my interpretation of table 52.3 ?

I understand that 521.9 applies which is what Davesparks is referring to, and I would never personally consider flex for fixed wiring, or less than 1mm live conductors for any fixed circuit, but the table does seem to support the OP's ideas.
 
It's a confusing grey area I say, I suppose, the bottom line to this is if the cable is suitably protected or not, I will reevaluate my usage of 0.75mm cable and use 1mm from now on.

as said, this is only to feed an outside light, I am not a silly billy wiring an entire light circuit up with it.
 
It's a strange one actually, Reg 422.3.201 says suitably protected against mechanical damage, but it's strange how it doesn't say a word about suitable protection if it's twin and earth which is just a different shape...

why should flex need any more protection than any other cable irrespective of the CSA of the conductors.
 
Last edited:
It's a strange one actually, Reg 422.3.201 says suitably protected against mechanical damage, but it's strange how it doesn't say a word about suitable protection if it's twin and earth which is just a different shape...

And different conductor construction, and insulation construction, and sheath construction.......
 
It's a strange one actually, Reg 422.3.201 says suitably protected against mechanical damage, but it's strange how it doesn't say a word about suitable protection if it's twin and earth which is just a different shape...

It's a fairly recent change in the regs which allowed flex to be installed at all, it was previously limited to 2 metres max length for appliance tails.
Every cable has to be suitably selected with regards to protection suitable for the environment it is in, regardless of what type it is.
 
Have you considered the max conductor operating temperature of the flex? A lot of it is rated to only 60degrees when fixed wiring and accessories are all rated for 70degrees. Will this make any difference? I don't know, but you need to consider it
 
Here's a bit of relevant history
14th edition
ImageUploadedByTapatalk1434751218.845910.jpg
13th edition
ImageUploadedByTapatalk1434751250.148634.jpg
 
Any takers about my post #8 and the regs stating a minimum csa of 0.75mm for the use of flex ?

I think it's open to interpretation.
I read it as the minimum size for a lighting circuit is 1.0mm and a power circuit is 1.5mm then flexes which are not part of a such general circuits (ie appliance tails etc) are restricted to 0.75mm minimum
 
I didn't know one existed, it's s shame you can't get 3A breakers across the different brands, o don't know if I'd have much need for one to be honest, but then there's always that once!

You get all different sized breakers across most decent brands. The lower sized (<6A) breakers are generally produced for panel and control applications as I understand it, they just won't be classed as 60898, or rather just 60898.
 
You get all different sized breakers across most decent brands. The lower sized (<6A) breakers are generally produced for panel and control applications as I understand it, they just won't be classed as 60898, or rather just 60898.

I did wander if that was the case Andy. But just had a look at the MK tech spec. See the approvals bit just below the table:



Screenshot_2015-06-19-23-51-52.jpg
 
I think it's open to interpretation.
I read it as the minimum size for a lighting circuit is 1.0mm and a power circuit is 1.5mm then flexes which are not part of a such general circuits (ie appliance tails etc) are restricted to 0.75mm minimum

For table 52.3 I would interpret this as meaning that if there is a connection to a mobile piece of equipment such that the connection needs to be flexible then 0.75mm² sheathed or non sheathed cable may be used.

Yep I must concur with you guys that the description in table 52.3 "for any other application" listed for flex actually should mean "for any other application than those listed above"
I have always worked to the 1mm for lighting and 1.5mm for power rule myself, just this thread prompted me to look up the table and question it. I also have never considered flex a suitable selection for fixed wiring other than for fused down circuit extensions.
Still an ambiguous table though in it's wording.
 
Hager actually do a large range in Type C which I suppose is quite acceptable to use on a normal circuit.

MCB 10kA & 15kA Type C MCBs

They should be available from most DB manufacturers, they won't be available for ranges exclusively intended for CUs though.

Can you use them for general/standard circuits? I see no reason why not, but undoubtedly someone will be able to come up with a reason why not.

7.5A was a reasonably common size once upon a time. I've seen a lot of 3871 MCBs in this size.
 

Reply to 0.75mm Flex into 6A MCB in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock