No Paul, this is your post No 24
You slipped the 'required' red herring in later, I assume when you actually read 521.5.1
Why do you keep repeating the word 'required' it's irrelevant. You either can or you can't bring the protective conductor through a separate opening.
Well I wouldn't want a 32mm grommet on the bottom of a CCU in a cupboard that a kid could easily get in to.
I'm really not following you here? Are you suggesting that we need to take account of bad parents when installing CUs?
(It's hard to resist making pedantic comments about goats here)
Haha... I don't see the harm of it being considered in a domestic situation for the sake of £13
You need to look at the definitions of earthing conductor, bonding conductor and circuit protective conductor.
On any electrical installation there must only be one means of earthing, thus the earthing conductor connects the installation to the means of earthing.
Now that could be any of the supply systems.
However, said earthing conductor then becomes part of the "sub-main" supplying the distribution board at the origin of the installation.
Now, regardless of where the supply originates from, or the means of earthing goes to, the Line, Neutral and earthing conductor connected between the means of earthing for the installation and the MET of the "first" "DB" in the installation all form part of the same supply circuit, thus they all must collectively enter any ferrous enclosure.
The same applies to any outgoing circuits.
Now bonding conductors are something totally different, they exist simply to create an equipotential zone in the installation.
They are not there by design to carry any fault currents within a supply circuit.
The distinction MUST be understood.
Thus they do NOT form part of any supply circuit, thus they are not part of the requirements of 521.5.1.
Therefore the earthing conductor of an installation is not an equipotential bonding conductor, thus, there are differing requirements for the three kinds of conductor.
Come on this is basic stuff FFS.
Did they not introduce a new Regulation in the 17th allowing a separate earth to be run along side an SWA cable?
Obviously the earth would have to enter the enclosure separately to the other conductors.
Read and understand the regulation number quoted in the OP and all will become clear.
If the additional cpc is bolted to the outside of the enclosure it is NOT entering the enclosure.
If it is entering the enclosure then it must comply with the reg, thus enter collectively surrounded by ferrous material.
This is not an option it's a reg, end of.
If you don't want to do it, put it as a deviation, else comply simple.
Why now though? For more years than I've been alive electricians have used a grommet or a bush for the job. If there was a problem with children (or goats) then I'm sure the IET would have given us a daft regulation to deal with it, they have after all create this nonsense about non combustible boards
The earthing conductor performs the functions of both cpc and bonding conductor. It is even sized with consideration to fulfilling both requirements.
You need to look at the definitions of earthing conductor, bonding conductor and circuit protective conductor.
On any electrical installation there must only be one means of earthing, thus the earthing conductor connects the installation to the means of earthing.
Now that could be any of the supply systems.
However, said earthing conductor then becomes part of the "sub-main" supplying the distribution board at the origin of the installation.
Now, regardless of where the supply originates from, or the means of earthing goes to, the Line, Neutral and earthing conductor connected between the means of earthing for the installation and the MET of the "first" "DB" in the installation all form part of the same supply circuit, thus they all must collectively enter any ferrous enclosure.
The same applies to any outgoing circuits.
Now bonding conductors are something totally different, they exist simply to create an equipotential zone in the installation.
They are not there by design to carry any fault currents within a supply circuit.
The distinction MUST be understood.
Thus they do NOT form part of any supply circuit, thus they are not part of the requirements of 521.5.1.
Therefore the earthing conductor of an installation is not an equipotential bonding conductor, thus, there are differing requirements for the three kinds of conductor.
Come on this is basic stuff FFS.
Why now though? For more years than I've been alive electricians have used a grommet or a bush for the job. If there was a problem with children (or goats) then I'm sure the IET would have given us a daft regulation to deal with it, they have after all create this nonsense about non combustible boards
So what does it bond dave?
It's not uncommon for a separate cpc to be required with swa when you get to larger csa armoured.
Depends on the earthing system I guess, but if it wasn't a bond then it wouldn't be required to comply with the requirements of a bond would it?
Seriously?Which regulation says there must only be one means of earthing?
It doesn't it must comply with the requirement of an earthing conductor, and depending on the means of earthing this has differing requirements, derived from ESQCR & BS7430.
Yes it is uncommon, a seperate cpc is almost never required with SWA.
The only time a seperate protective conductor is normally required is to fulfill the requirements of a main bond.
It's not uncommon with larger sizes Dave, over 50 or 70mm.
It is uncommon for it to be required, this is not the same thing as not being uncommon to see one installed. If is very common to see a seperate cpc being installed unnecessarily
View attachment 29571
Where PME conditions apply the earthing conductor must meet the requirements of a main bond.
For the other earthing systems the earthing conductor automatically meets the requirements obviously
Spoken to the NICEIC today. The context of the appropriate protective conductor in regulation 521.5.1 doest include a main earthing conductor as its not part of an a.c circuit in bs7671.
dont shoot me its just what ive been informed!
thats what i was getting at earlier.But the metal board will be earthed....
But we are on about the main tails and earthing conductor... Not a cpc from a circuit
.... and its good to know that electricians differ completely.
thats what i was getting at earlier.
there is no need to have the earth going in the same hole because it is at the same potential as the case.
unlike L and N which will be at 230+ potential to the case/earth