Guys, I'm not new to the trade, I know what my meter is testing and I'm not just pushing the button and hoping for the best.
My meter does not give me the option of 3 lead test or 2 lead lest although it will carry out the test with two leads.
P-le on low or hi
And p-n on hi only.
I have been testing correctly. I came on here to see if anyone has came across anything similar
Not yet Dave I'm there tomorrow and will keep you posted
I've tested every circuit individually from start to finish. Every circuit trips the rcd with no others connected. The cooker circuit even trips it with nothing connected. Ir shows up clear on every one. Get to zs and it trips
Back to the OP - given its a 17th Ed CU, what does your tester do with the 2nd RCD?
It is a 17th ed cu and if I'm testing a circuit covered by that rcd it still trips. Doesn't matter which circuit covered by rcd 1 or 2 it still trips.
That answer does not make sense!
Are you saying BOTH RCD's trip?
Have you tested your tester on another RCD?
Yeah I just read the manual, interesting.
I also noted how the manual talks about the possibility of RCD tripping even on low current tests, the possible cause and that an alternative method may need to be used.
I guess the OP didn't bother to read the manual for his tester!
Thing is Dave it's never happened before and I've tested many circuits/properties. Why now???? Why the 2 rcds????
It doesn't trip the 2 rcds. It trips the rcd to which that circuit I'm testin is covered by. Make sense??
Most likely answer I think is a N-E fault somewhere in the installation.
Unless it's got a different type of RCD installed, either an A or B type instead of AC?
Try clamping the tails to see what leakage is there before you test as even on No Trip your still injecting 15mA into the cct so you may have a leakage which puts the RCD above its Ramp value just a thought!
Thanks Tony at last some decent advice. Thank you
jord35davies,
brianmoooore,