Hi all , i am new to these forums so please bear with me. I am needing some advice on what to replace for this fault.
I have a relatively new garage consumer unit made by MK . 5 way unit.
It has five seperate mcbs and one rcd.
I have six flourecent lights. Each on a separate switch.
But two of them are on a two way set up. Where by i can switch them off at the front of the garage, and back on again from the back door of the garage individualy.
So two of the lights are controlled by two two way double light switches.
The problem is some times but is starting to happen quite frequently now when i switch one of these lights off it trips the rcd off inside the garage consumer unit. Switching all the power off inside the garage.
The flourecent lights are only a few years old. They are 6feet 70 watt single flourecent battens with starters made by crampton cbl61t model
The switches are good quality mk units.
The switches at the back door of the garage are ip60 weather protection switches. They are 3 double switches.
The switch at the front of garage is a double mk switch.
I was getting a arching sound from the front switch when i switched the lights off, so i have changed that and it has made no difference. The rcd still trips out.
I have narrowed it down to one or both of these two flourecent lights causing the issue. Because when i switch on and off again the other four flourecent lights from the back of the garage the rcd doesn't trip .
It can not be a faulty switch at the back of the garage as one side of the switch is connected to one of these four good lights and other rocker to one of these suspect faulty flourecent lights.
I have disconnected light 1 from the circuit and tried switching the othet light on and off again in the the garage and the result was it tripped the rcd. So i thought it must be the other flourecent light fitting that is faulty? So i Reconnected the first light fitting and disconnected the second. Result was it still tripped the rcd in the garage .
So i disconnected both flourecent lights from the cicuit and fitted two single light pendants with 60 watt bulbs .
Result was when switching the lights off the rcd does not trip out.
So would replacement of these two flourecent fittings with newer HF versions be the solution and i have two faulty fluorescents which i think is doubtful? Or is the fault with a over sensitive RCD as it doesn't do it all the time. Should i replace the rcd with a higher rating unit ? But the current one is rated at 63amp.....
I am thinking of connecting the suspect flourecent light fittings to a piece of 3 core cable and putting a plug on and trying them in a socket to see if they trip the socket breaker then i will know for sure they are faulty ?
My thoughts are its got to be either a oversensitive rcd, but its doing its job or one or two faulty fluorescent battens.
Surely i would expect the mcb in the garage consumer unit to trip out for my lights rather than the rcd in the garage unit.
fluorescents are notorious for tripping RCDs as the ballasts have inherent leakage, usually though with more fittings than you 2. however, with then being 6ft., it could be the cause. also the may be cumulative leakage on other circuits, each below the RCD threshold, but adding together. I would replace the 2 suspect florries with LED equivalents, or modify to LED tubes.
MK Sentry
80 Amp 100mA RCD 2 Pole
Residential 6kA Residual Current Devices (RCDs)
should i fit a bigger rcd unit to this one from a 65 amp ??
No
It’s 63 amp not that it matters as you’ve obviously a fault which is tripping the 30mA threshold of the rcd.
That or it’s over sensitive.
How did you test the rcd?
What test kit do you have?
sorry , no test kit , just pressed it and it resets . i think i might need to get a electrician in as its very annoying this ,
the thing is my parents garage has the same set up but has a old style plastic 10 way consumer unit in the garage with exactlty the same set up with lights etc and there is no issues with the rcd tripping out .
5 page thread ................. are you mad.
Only test kit and knowledge how to use it will fix this issue...
Change the fluorescent to LED tubes and bypass the ballasts, would suggest you get an electrician in to do it as they will know what they are doing and can then do some proper tests. Your analogy of your parents setup being similar to yours is like saying I have the same consumer unit as my neighbour but can't understand why mine has a fault and theirs doesn't!
Without proper test equipment you are peeing in the wind. I've just read your 5 page thread on another forum...The fault should be found 1st before you just start replacing things. Your methods are haphazard.
agree , but I was wanting to fix it myself however it is really annoying its looking like i am going to have to get some one in as doesnt sound like a easy fix. its also annoying that my parents garage has the same kind of set up but has a old style 10 way unit in the garage and there is no issues .
led lighting at the moment to change all the lights to this set up i think will be too expensive . i think i have a look for a electrician next week . i am just very cautious now with trade people as have had a few bad experience with so called time served specialist in the past that where vetted etc . but looks like i be going that way again and getting some one in ..................
that's probably because the neighbours had their install done by a qualified spark.
no, strangely enough i did it 10 years ago , but now since you are not allowed to do most domestic home electrics yourself i had to pay a qualified part P 17th edition sparkey to do the job . the irony of paying a specialist ,and having it tested and needed to keep the installation certificate etc for insurance and now its faulty and i am a home owner annoys me . whats that saying a trades man never blames himself its always his tools . check a trade.com
i wouldnt care the flourecents in the parents garage are at least 10 years old and had no problems what so ever with them or the old plastic mk 10 way consumer unit . this stuff in my garage is only a few years old . what a joke ...........
i
t only happens when switching one or both of them off ........shouldnt it happend when switching them on? why doesnt it do it with the other four light fittings when i have them all on and switch them off??
I recently completed a garden lighting installation. 5 CFL bollards and 7 LED spike lights. The day after completion customer messaged me telling me it was tripping the RCD in the CU supplying the installation. It appeared to be that this was happening when they were being turned off.
Everything was tested on the day of installation, no excessive leakage, great IR readings, RCD ramped OK and was working great. Tested again the next day just in case, nothing even hinting at a cause was found.
Scratching my head I systematically went round the lights checking everything. The only thing I found was that some connections in the bollards were loose (these were manufacturers connections not mine).
Tightened them up and the tripping has stopped, so my advice would be turn the power off and work through the connections in the fluorescents making sure they are nice and tight and see if that fixes it.
I'm not saying there are other problems that proper testing would reveal, but as an interim measure, start simple and check the connection.
But you are allowed to. Anything but installing new circuits, consumer units or work in bathrooms does not need notification.
You need to test your own work, of course.
But, really, as has been advised over and over again, change out those two fittings. You can do this yourself.
If the problem is still there, then you need an expert.
Best idea to date Mr Karl get a Sparky to test your garage and locate the fault.
Where abouts are you? There may be reputable member of the community here who can help or know someone who can?
he's in Redcar where they race women and marry horses.
just annoying thats all , but your comments are fair enough . seems to be a totaly agreement that the flourecents are old school and i have been unfortunate . might as well just change the whole units to led . any one recommend a good quality make as heard they are some cheap rubbish ones out there . i dont want to buy cheap rubbish and have to do the job again in a years time or so . thanks
Another cheap option to try is replace the switches.
Closing a double pole switch may also trip an RCD (as may closing a single pole switch). The effect may be aggravated further by the slow break feature of the switch often found in domestic a.c. switchgear.
(Beama RCD Handbook)
Switches are relatively cheap, and easy to replace. Might be worth a try, as your other luminaires don't seem to have the same problem, with their respective switches?
Try what SparkyChick suggests first.I think you might find that's the problem especially with you saying that you could hear crackling.Also check the busbar under the breakers.(After isolating the unit!). I use my mobile phone camera to look along the breakers and make sure each one is clamped onto the busbar.It's amazing how many times the breaker connection has missed the busbar and is just touching it instead.
thanks for the replies so far. yes lol am in redcar . near race course lol
have replaced the switch at front of garage . i check loose connections on the two light fittings.
any good sparkeys in this area ??
got to be a fault on the two light flourecents ?? evidence seems to be going that way and all saying on here and elsewhere flourcents suck.
have checked connections already on garage consumer unit and all are good.
if i switch one or both of the suspect lights off on average it will trip the rcd 3 out of 10 times , so its a annoying fault. its on this cicuit as it doesnt do it now since temp fitting two light pendants with 60 watt bulbs in. which goes back to original comments made by people on here and elsewhere its the ballast on the flourecents discharging on switch off?? thanks all for your help so far , very much appreciated and listened too.
you posh git. i use a candle and a mirror.
whats the best make on the market at the minute for 6 feet led battens for quality and reliability ? I post thus question on a new thread as well. As worse case scenario here for me is i up date these flourecents to led specification and the fault is still there .but i be saving and improving the lights in the long run regardless of whether i get a electrician out to have a look or not if fitting led battens doesn't fix the issue.
Are knightbridge a good make??
Hi,have you watched the episode of "Father Ted",where Ted is explaining to Dougal,that "these" are models,and "those" are far away...?
If you are continually adding and altering an already faulty set-up,you will be complicating any testing which will be required,to find your fault(s). :)
That is a bit of a hard question as even the so called premium brands are buying the leds inside off the open market and a lot of the lights regardless of brand and packaging are made by a handful of companies with pretty much identical parts. I have fitted numerous LAP led battens from screwfix and had no issue. quick and easy to install with screwless connections inside.. its about the only good thing in the LAP range mind!
before i replace what i believe to be the failing flourecents causing the rcd to trip i am going to swap around two of the four lights that are working to the circuit with the suspect flourecents on . if they work on this circuit i will know they are faulty and will replace with led versions instead . as it wont be any think that has failed if this test works. as the circuit works with normal pendant light with 60 watt bulbs in no issues. so i dont think it wiring fault .
if this test fails i am going to get a electrician in to test the circuit and measure resistance etc as done all i can as a home owner to find this fault without causing any harm.
Redcar
Garage consumer unit rcd trips out
Lighting Forum
Mr Karl E Taylor,
Mr Karl E Taylor,