gave me a invoice which simply says tested garage electrical sytsem.
i was there all the time whilst he was testing it.
used a clamp meter and another device of some sort which he can put up to 500 volts on the system etc if that makes sense .
gave me a invoice which simply says tested garage electrical sytsem.
i was there all the time whilst he was testing it.
used a clamp meter and another device of some sort which he can put up to 500 volts on the system etc if that makes sense .
New
gave me a invoice which simply says tested garage electrical sytsem.
i was there all the time whilst he was testing it.
used a clamp meter and another device of some sort which he can put up to 500 volts on the system etc if that makes sense .
When I do such fault finding I give a more detailed description of the tests under taken AND the results of such tests.....
This is helpful for you, the tester if they come back, or a subsequent sparky - and is especially relevant if you don't isolate the cause of the problem.
The two of the six are they wired so they both switch together on two way from each door have I interpreted this correctly? And is it a correct statement that it is only when you switch this bank of 2
lights it trips the RCD
gave me a invoice which simply says tested garage electrical sytsem.
i was there all the time whilst he was testing it.
used a clamp meter and another device of some sort which he can put up to 500 volts on the system etc if that makes sense .
he said he tested the rcd and it worked fine and is ok .....
An EICR of some sort for that particular circuit, or at the least a report with readings as you rightly pointed out. Although it would be fairly simple to issue an EICR for the circuit in question, may be OTT but at least it would show some pride in the Electricians testing regime, may not be the document the IET prescribe, but then there are no certs for repairs / fault finding is there, remember it's been a while since I was working, so there may have been changes, what sort of paperwork do you all use when you get called for a fault? if there is nothing then maybe something the IET should look at. Grateful for any thoughts.
The two of the six are they wired so they both switch together on two way from each door have I interpreted this correctly? And is it a correct statement that it is only when you switch this bank of 2
lights it trips the RCD
Yes one of them did .so i swapped it over from one at the front of the garage and the other one to the one at the back of the garage taking them both off this 2 way circuit.
Made no difference it still trips the rcd with the light swapped over.
So my hunch is now they all have live supply going to them regardless of the switch and its the discharge going back to earth from one of them causing the rcd to trip out