Hi,

I have an looking to replace some plastic surface switches and I have noticed that there is no earth wire.

So I don't think I am going to be able to any metal fixings.

What are my options.

  1. Just leave it as it is.
  2. Look to get the circuit re-wired.

Thanks
 
Was that also the case under the old 16th?
The singles that I ran in were insulated and sheathed, as I needed to pick up some live feeds and also at that time it cost less than g/y singles

Not 100% sure about the 16th mate. I'm sure someone will be able to tell us.
 
Had a feeling it would be, the 16th was very earthy, equipotental/ simultaneous, sinks, windows, radiators - its a lot easier these days :)
Well I got around 543-01-01 by using insulated & sheathed singles..

2.5mm is the minimum size if mechanical protection is provided so your 1mm cpc is non compliant even if you do allow the sheath as mechanical protection.
 
Question people. When you install a 4mm earth, how do you go about connecting it to the light fittings? I thought it would be too big?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
No Earth in light circuit
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
35
Unsolved
--

Advert

Thread statistics

Created
midiman,
Last reply from
Pete999,
Replies
35
Views
8,123

Advert

Back
Top