It isn't. The cooker is on a 32a. It is in conduit for approx 1.2m then is clipped direct to the skirting board before chased into the wall to the socket (don't ask, I didn't install it! ?) Total length of the cable is approx 2.5m to the switch then approx 1.5m to the cooker terminal.
I worked out the load as it is a 7.43kw cooker.
So taking diversity into account the 6.0 & 32A is more than sufficient as it is 10A +30% of remainder (22.3a) = 16.69a + 5A for the plug socket on the switch = 21.69A.
6mm in conduit is rated to 38A & 34A once in the wall. So it's well within spec.
The 6.0 40A is supplying the garage and that is clipped direct.?
Apologies my error.
Very tidy job - well done. BTW looking at first photo of new board did you originally have it too close to the ceiling to get the cover on ;-) Most of us have similar at some point!
I have a Fusebox board sitting here - I'm fitting one tomorrow for the first time.
I'm impressed with it so far. The cover has screw catchers, the knock outs actually knock out, and it feels very solid. It's also a nice size to replace a 6 module rewireable Wylex if space is limited.
I very nearly did. Then luckily had a flash of wisdom.
The board is very nice and good quality. I was impressed with it myself. Just irked my CDO with the slight lean.
Very good first CU change @Raptor0014 ! Did you have a moment of worry when you saw hundreds of cables sticking out of the wall, with you the only one responsible for putting it all back together? ? I still remember that feeling from my first CU cjange.
Also very brave to put it online as every minor detail will be examined and criticised, still I guess that is what you want for learning purposes.
@westward does have a good point about the 6mm in conduit though, on a 40A breaker. I'm never too sure which reference method takes preference though when only a very short run is in the more strict reference method.
I will add reg 521.5.1 . I believe the main earth should enter through the same hole into the CU as the line and neutral tails, to negate possible electromagnetic effects. I stand to be corrected though. If I am correct then I will be chuffed that I spotted it before @westward10
Nice n neat good job ??, with regards the high readings I generally find fusebox pretty consistent with the trip times unless it’s a type A then they get abit close to maximum ?
[picky]B40 first on the busbar, not last.[/picky]
That was what I initially intended to do. But the way the cable run had been installed left it with no play and I didn't have time to take the covered walkway panels down, unclip it and see if there was enough play to move the RCBO nearer to the switch.
In reality I doubt the garage would ever pull anywhere near 40A. It's only got sockets and lights at the other end.
Can you give a valid reason for this.
used to be usual to put the highest loads closest to the main switch. the reasoning being that the larger load currents didn't have to travel further along the busbar. no logic behind it, it was realised about 30 yearsa go that the electricity did not leak out proportionaelyt to the length of the busbar and this pracice was stopped along with the old wives tale of "exporting the earth".
See my other post, it's not in conduit.
Noted ref the earth.
And yes correct, this is why I posted to ensure I continuously improve myself. Nobody is perfect as they say.
I'd always understood that highest loads should be placed closest to source of supply and accepted that without question. In the last few years I've read opinions that suggest there is no reason to do this and that it is better to populate a board by ensuring higher loads are separated to allow efficient dispersal of heat.
Not really in a position to comment, but the latter makes more sense and I'd be interested to read thoughts on the matter.
i agree. i never place 2 High load MCBs adjacent.
Type AC are being phased out it would seem. I only fit type A these days.
Stopped fitting them years ago. I don't personally see any merit in fitting Type AC anymore. For no (or minimal) extra cost with many brands it's a no brainer. That said, the FuseBox ones are substantially dearer than their Type AC, but thankfully I think they might be withdrawing the Type AC. There are neutral switching Type A compacts with FuseBox - so these are what I use when using that brand (although they are dearer).