Got called to "a flat in Manchester has no hot water" at 16:30 today and to be frank I was a little miffed to have to attend.
So arrives at site, spends 20mins finding parking, 30 mins finding the site contact, getting keys and then being informed that it was not one flat but eleven.
Have no idea what the supply is, big I'd guess, nor did I have access to ant distribution equipment, just a list of flat numbers.
So I go to the first one. The 16A MCB was off and was informed that "it goes bang if you try to turn it back on" which I took his word for.
So I worked back from the tank, element OK, thermostat OK, wiring OK however the timer was visibly burnt out.
Did a random sample of the other ten and of the four I checked out all had the same burnt out timer.
Due to the time nothing more was done and an assumption (I know?) made that all had blown.
The only other thing I did was to check the local voltages and all were 236-7V and steady, for the brief time I observed.
These flats were all over, not just one floor so unlikely to be from a single phase or distribution board.
The tennants all made the same complaints of flickering lights and one long recent power outage.
None of the staff had any knowledge.
----es me off that there is nobody on site with any ownership, or understanding of the buildings and their systems, there are two blocks approx 400 flats for christ sake.
I'm half tempted to just replace the controllers and note there may be underlying issues that need further investigations.
How would you guys approach this?
Most certainly not replace the controllers .without a lot more testing Unless a whole batch is crap etc ? First port of call would be to check if the controllers have been fitted correctly .Could be lose terminals ??
They're all, the four I checked, sound and correctly wired.
My concern is that the recent power outages have had something to do with it but with out communication with whomsoever resolved that issue, if indeed they did, and to confirm there is causation not just correlation then it's just stupidity to proceed, I know that.
It just baffles me that these building, under the management of a bunch of kids more interested in filling "units" than the safety of the tenants, are expected to manage themselves and you as a tradesperson should just be able to come in and "fix it".
Does anybody there even have the knowledge to comprehend that the have a potentially dangerous situation?
The more I think about this the more exasperated I get.
Best guess, loss of neutral
but as said before, some proper testing over time might be required.
if you change them as requested, ensure that on the invoice you recommend an urgent assessment of the building supply and distribution wiring as you believe there may be an underlying fault that caused the failures
It is often possible to identify the root cause from close forensic examination of the damage. Is there any way you can get and post high res pics and / or get a sample open on the bench and take some measurements?
Terminal burnout is not normally caused by a supply fault like a floating neutral. It is more likely to be from incorrect installation or faulty units. Overvoltage will usually kill the internal DC supply dropper and one can often tell from which components failed in which way, whether it was a 'surge' or a long low overvoltage from a floating neutral.
Your quite right, it's time to get CSI on it.
The fact these faults have occurred across most floors leads me to lean towards a supply issue or early distribution issue.
I'll try to get back there today and swap out a couple, get some better pictures and do an autopsy.
I would contact the manufacturer, ask them if an almost 6% failure rate is normal, wording the conversion well, I have no doubt they will ask for one of the failed units and do the post mortem.
Especially if you highlight that even if there were some form of supply problem, it didn't impact anything else other than their timers, nothing from other supply equipment/other makes of timers through to sensitive electronic equipment, only their kit.
I missed the rating bit of the timer. This is important
They are rated at 16A. The hot water cylinders are on a dedicated circuit off their own 16A MCB, isolated via a 20A double pole switch, length is a couple of meters.
Couldn't see a rating on the element but looking into that now.
Edit to add,
The elements are 3kW but looking at the plumbing I think they're on a central hot water system as there seems to be a coil on the cylinders.
I'm back there tonight two replace a couple and grab some more info.
Edit to add,
I would also see if the affected units are on the same phase still can’t rule out floating neutral
Might be hard to tell now, but what were the terminations like?
im thinking these were all fitted when the block was new, just wondering if maybe the same- not very effective- electrician did the connecting and left a loose screw in these particular flats.
clutching at straws, but always something to think about if all other avenues of investigation are exhausted.
Has to be a factor.... The ability for someone to just make a mistake/miss something is super high
Possible but it's the time frame that leads me away from workmanship, coupled with the recent other electrical issues.
I don't know for sure but the block looks to be ten year old and for bad workmanship to start to show up so late in the day then all within a week makes me think other factors are at play.
Here's some photos @Lucien Nunes and others.
The terminals and cables are clean as a whistle.
This is the culprit
Capacitor(?) has blown.
Edit to add,
Would definitely clamp it , you may get over 14 Amps if lucky...lol but is stuff that good nowadays. BTW i only use Timeguard products for this type of stuff as fed up changing crap out after a few years
Looks like a metal oxide varistor connected across the supply, If several blew at once this is a sure sign of overvoltage on the supply. A MOV is normally high resistance, but it's resistance drops as the voltage increases to stop voltage spikes. A sustained overvoltage such as from a supply fault will quickly overheat and destroy an MOV.
Would definitely put my money on a floating neutral as some stage some Dno have a search function on there site to advise if there have been any incidents in the locality
Yup, it sure does look like an MOV that wasn't big enough absorb the available energy in the overvoltage event. When that happens, it can initiate an arc that lasts until the fuse blows, which can dissipate so much more energy that it makes it hard to identify whether the trigger event was an impulse or a prolonged excursion above clamping voltage.
Assuming the building is served by conventional urban underground distribution the latter seems the most likely and I would say the likelihood of a cable fault causing both the timer damage and the flickering / outage events was very high. Other items in the properies with MOVs (and even SPDs) might also have been compromised, but if the MOVs in the timers had a slightly lower clamping voltage then they might have all gone phut before many of the remainder showed signs of distress.
The sub might be specific to the estate or building, in which case any information you can get from the DNO about recent faults might nail it.
My thinking of what we have so far.
The catastrophic failure or the MOV (thanks) in the controller would point to a large over voltage situation.
It is most probably not environmental but a lost Neutral.
Without further information this could be anywhere internal or external.
So I was thinking to approach it on two fronts, to contact the DNO and report a possible Neutral fault whilst surveying the site, reported faults and drawings to see if a pattern can pinpoint the location.
So in a normal fault free situation the installation should look like.
If the fault is in the below position then I should only be hearing of power outages in flats 7, 8 & 9 but not over voltages or the MOV failures I'm seeing.
If the fault is in the below position then flats 4, 5 & 6 and flats 7, 8 & 9 will see voltage fluctuations between 0V and 400V depending on their respective loads, this situation could cause the MOV failures.
And finally, in the below image the fault would be evident across all phases and all flats with under and over voltages. Whilst there are sections of the internal installation that could contain the fault; in this scenario the fault could also be external.
Ii actuality I have already informed the client of the liklihood of a serious fault existing and that it may be internal or external and they will be picking it up from here.
I'm quite disappointed really as its quite interesting to see how far you can fault find on paper if you have enough information.
Your explanation of the possible scenarios is correct but the configuration in pic.3 is unlikely to exist in practice. Each single phase service will be derived from a 3-phase busbar, with neutrals normally serving one or three phases but seldom two.
If the fault was a cable strike, the neutral may have not merely been broken but also shorted or arced over to a line. A variety of different voltages may have been impressed on the loads in quick succession as the fault developed.
I don’t think the burned out disc is an MOV. The timer uses a transformer less way of producing low voltage dc to operate the electronics. I reckon one can see a bridge rectifier - the white block component, and a disc capacitor in series with a resistor of suitable power rating together forming a mains to low voltage dropper. The placement of the resistor and the disc capacitor makes me think their right hand ends are connected to Lin and Nin respectively and their left hand ends to the ac inputs of the bridge rectifier which are normally the inner two leads for this style of rectifier. There is a smoothing capacitor to the left of the bridge rectifier. I reckon the gold rimmed cylindrical component above the relay is a battery for keep alive in the event of power cut and accumulator to handle short duration current surges when the relay turns on.
A picture of the underside of the PCB would be handy.
The white block will be the dropper capacitor, the bridge rec will be SMD. But yes, let's see some pics of the PCB
Block of 200+ flats, eleven single channel hot water timers blown this week alone.
GBDamo,
Simon47,