I guess we shall find out when my "incompetent" --- gets a multi-function tester on MondayActually thinking a bit more - if there is a N-E fault downstream of the 30mA RCBO it should also trip as it would see the imbalance as well. That assumes the trip speeds are selective, is the 100mA one a delay RCCB (i.e. "type S" for selective)?

Don’t take it personally! We have to assume that unknown people can’t test safely. In colleges testing is taught after installation and after experience has been built up with how things are typically wired.I guess we shall find out when my "incompetent" --- gets a multi-function tester on Monday![]()

A good start to the day!Well, I am still alive.![]()
Something like this is needed:So I managed to find my clamp meter and it is showing 0.15A to 0.5A on the 20A setting depending on if I clamp near the RCBO or the main tails where the 4mm cable is accessible.
Don't think one can trust it... Ideally need something that measures in the 2A range. Will be worth it in my electronics lab so I will grab one tomorrow.
Good to hear.Got my hands on the multifunction tester. A pretty good bit of kit to have a play with. Found a fault on an old extension cord (not been used in years) so that has gone in the bin so already paying itself off.
I did the RCD tests on both AC/AC+DC settings. The 30mA RCBO for the sockets was fine as was tripping within spec.
If it is type AC and tested on a type A waveform with DC component then it can be desensitised.The 100mA RCCB tripped at a max of 105mA on AC and at 450mA on AC+DC. Not 100% sure about those results.
Those are massive currents! Is that measured with L&N in the clamp, or are you (incorrectly) clamping the CPC? If so then any metalwork anything is in contact with could be causing odd currents to circulate.I did an IR test on the board between N+E and L+E * 3. All fine.
Having been messing around with all the plugs and sockets (mostly extension cables in the office area), I have reduced the apparently N to E leakage down from the average reading on the socket circuit of 0.4-0.5A to 0.1-0.2A.
Put a few new 8 way extensions in while I was down under the desks which might have helped?
OK.I did do an IR test on all the existing multi-way extension cables and all were fine on 500v.
Have you IR tested the power supply? I.e. the sort of basic PAT testing part (along with CPC bond resistance, etc)The RCCB has yet to trip under normal conditions but as soon as I put a load on my benchtop AC to DC power supply, it trips.
Could be a fault with that bit of kit but that kit is not normally plugged in. I tested it at home and the RCD did not trip there.
Something like this is needed:
https://cpc.farnell.com/multicomp-pro/mp780050/mini-leakage-current-tester/dp/IN08364
Also you need to get the L and matching N in to the clamp to see the residual. I would strongly advise against moving cables in an energised DB! Try and get anything to measure in-place and accessible with all power off.
If it is type AC and tested on a type A waveform with DC component then it can be desensitised.
If 100mA rating it ought to trip between 50-100mA. You need to have all loads off so you are just testing it alone, and not having system currents also present.
I am clamping the Live and Nutrual 4mm singles coming out of the RCBO. It ranged from 0.2A to 0.7A but it really came down to how I was holding the clamp meter on the cables and at what angle. That is why I don't believe my 20A clamp meter. Will wait for the one from CPC to arrive.Those are massive currents! Is that measured with L&N in the clamp, or are you (incorrectly) clamping the CPC? If so then any metalwork anything is in contact with could be causing odd currents to circulate.
Have you IR tested the power supply? I.e. the sort of basic PAT testing part (along with CPC bond resistance, etc)
Are you sure the power supply is going in to the RCBO's supply? There is something inconsistent with being able to trip the 100mA incomer and not trip the 30mA socket feed, unless the installation happens to be sitting only a few mA leackage below the trip point normally.
Check the general leakage to see if it is close to the 100mA RCCB's trip threshold.There are only 3 circuits on the DB. Sockets, Door and Lights. I can follow the 4mm singles from the sockets up into the RCBO.
This is the reason why I am struggling to get my head around it all.
It has an S on the front off it.Check the general leakage to see if it is close to the 100mA RCCB's trip threshold.
Check that the 100mA RCCB is a delay type (S), otherwise a very short spike might just trip it before the 30mA one goes.
The half-decent leakage current tester arrived today and it is very good. Very nice build quality for the price.
So I tested a load of stuff and my space heater, is leaking around 60ma. My LED lights/printer/network/IR heater circuit is leaking around 30ma.
Without these two circuits, my leakage is down in the 3-5mA range.
With these circuits, it is in the 100-125mA range for the whole DB.
So I guess we have found the issue. As to why the RCCB trips and not the RCBO, no idea.
The RCBO is 30mA and the RCCB is 100mA.
I tested the RCBO and it trips fine on the Megga multifunction tester. The RCCB trips at 110mA.
I have done an IR test on the space heater and it is fine up to 500V.
Think I will retire that anyway as it is on recall apparently...
Will go through the other circuit at a later date to see what in that is causing the 30mA leakage.
It is odd to see 100mA leak and no DC effect, unless there is some largish capacitor in there! Or maybe something odd happens when it gets hot. Either way, that is a rather sick heater!
As you are running close to the up-front RCCB's threshold the trips make perfect sense. Without the heater can you now plug in stuff, etc, and all is happy?
OK.I will remove the heater from the circuit when I leave and see if it trips overnight. I have removed all the plugs from the sockets before and have had it trip so I don't know if this is the only issue here.
Have you opened that socket to inspect it? Or try a new one?But as soon as I plug in my office equipment (Laptop, speakers, monitors, phone etc) and it trips. These were only adding 5mA earlier.