Darkwood
Doing an EICR and found this. Newish build too at 3yrs old. Owner never had any paperwork prior to today and it’s going to be rented out.
Novel way to use a cooker socket for a gas hob igniter. So the gas hob is on a 32a circuit of its own. Plug wired in 6mm
Cooker/oven is on its own 16a radial with the fridge.
The socket is fed in 6mm from the cooker circuit right? And the hob has a plug with a suitable fuse fitted?
The socket is the cooker circuit. It’s had the outlet plate swapped for a single gang.
Yes the plug has a suitable fuse in.
Not saying it’s a problem. Just an odd way of doing it considering that’s how it was done from new.
Yep, nothing wrong with that. All the houses on my 1970s built estate were the same, ie. wired with a 30A 6mm circuit to a single 13A socket in the kitchen. The option was given when buying the houses of whether you wanted a cooker switch fitting instead of the socket.
We have our fridge plugged into ours (cooker is gas).
I think you'll find this is simply the 'ramp' system. You see how it's all B6's then a B32 on the end? The slanted bus bar is so the power can accumulate from left to right to run the higher powered appliance on the 32a breaker. We call it 'upramping' in the 6-week-wonder world.
You have to wonder why the false ceiling was put in anyway, probably a public building that needed either reinforcing for it use above or fire rating, sound proofing, but that still does not explain the off centre light fitting, they went to the trouble of putting in a drop bulkhead to keep the rose exposed, but then why?????????
This is a relic. Not sure what the RCD is supposed to be protecting as not a single thing in the property that I’ve tested so far will cause it to trip at 1 or 5x 🤷🏼‍♂️. Test button works ok though. 😂
I’m aware now it’s a VOELCB and is considered obsolete. Thanks Tim, DPG, Westward and everyone else who replied.
Then I found this. First time I’ve seen a socket tried to be fixed with blue tack! Guessing they got annoyed and smashed the back box off as it wouldn’t hold. 😂
As you probably have found out by now, the VOELCB was the predecessor to the RCD but worked on a totally different basis and one that is now considered quite unreliable and long overdue for replacement.
However, the twist in that particular tale is some forms of EV open-PEN detection work on the same principle of observing a CPC to true Earth voltage!
8K
Darkwood,
UKMeterman,
