What was even better was the property has an old 16th Ed board with no RCD for any circuit.
Maybe this proves RCDs and CPCs are overrated. 🤔🤪
Did you try a Zs at all just wondering what it was if you did.
Reactions: Baddegg
No earth. No rcd.
Gonna try polarity for the unholy trinity.
New build, SWA supply from meter to CU
All the flats have been done the same
no gland on SWA the other end either
what a poor job
what a poor job
I agree, what a bodge for the price of a box and a tail gland.
That is poor.
so many ways it could be done better
Reactions: timhoward
Is that a MI supply feed? How is it terminated into the isolator?
Orange SNE and concentric cables aren't uncommon.
Have them in my place of work. But just wonder how they are terminated, is it just like a conventional mineral insulated cable?
Nearly every earth extended, including main going from 16mm to 10mm. Neutrals crossed over on the ring circuits (ie neutral for one ring with neutral of another in the same terminal), most of the live terminals are loose. I could go on.
But otherwise, not a badly installed board….. 🤣
Reactions: Jim_e_Jib
Correct it isn’t. But I’m replacing the CU tomorrow so that will be corrected. 😇
Erm, I think someone got the wrong idea when interpreting the advice with single phase use of swa cores.