OP
pushrod
is it not 24.73amps
approx 24A is Ib
Load is probs inductive so 32A type C or D MCB
Discuss cable sizes in the Electricians' Talk area at ElectriciansForums.net
is it not 24.73amps
so how would the layout work then can u explain of where the come out from the DB ?
whats the run?
Im off to the van to get me book
huh 6mm that what i got from 30A 6mm??
Think your all wrong here . 50kw is 217.39 amps split over 3 phases , 72.46amps per phase. its oven resistive load. nearest breaker 80amp triple pole . instaled in trunking ref meth 4 , 3or more cables . requires 35 mm cables. rating 89amps. from quick look . night all. Michelle.
so how would the lay out work? i take it its just ran out the CU
you have been a great help thank you very much
he has done 50Kw / 230 /3 hasnt he
brain in gear (just)
50x1000 50000
1.73x400 692 = 72.25a ( no correction factors taken into account)
wat type mcbs for motors?
cheers mate