Guest viewing is limited
yes, as long as installation methods regarding ccc are compliant.
Ok thought I'd check rippEd off board and only radials I'n it 2x 2.5 and 2x 4mm
This isn't the norm obv sockets are all radials is this ok? As its not good practice to do so is it?
nothing wrong with sockets on radial, as long as the cable ain't overloaded.
Thanks mate well board done now going to test, what's max zs for a 4mm mate??
maz. Zs is dependent on the MCB, not the cable. 1.44ohms for a 32A type B. ( 1.15 with the 80% correction.)
They do them in a star configuration I heard from a visible JB in France. No rings there :)
Another job done and tested all good readings!! Had to change two faceplates on down radial as wasn't getting my r1+r2 readings
Bring it on...death of the ring cant come quick enough.....(note....spent 3/4 of a day today trying to find a break in ring continuity on the lives of a ring....PLASTERED IN JOINT in a flush box with cardboard cover...connectors....obviously wouldnt of happened if he'd used wago's:rolleyes:)
How did changing the faceplates help your R1+R2 mate?....dodgy switches?
sockets in property approx 20years old, they give false r1+r2 readings, so i just change them first reading 1.42ohms second reading 0.22ohms !! more like it!
They thought of this a while back when trying to get rid of our 13amp sockets & using 16amp sockets. Other countries dont have ring mains. I have wired kitchens on 4mm2 or 6mm2 radials, saves worrying about any overloading when you'r not sure of appliances. I rewired my bungalow & have no ring mains. 20amp radial to bedrooms, 2 x 20amp radials to lounge & dining room & 2 x 4mm2 radials to kitchen = 6mm2 for cooker, regards piccollo
if you dont know loads, what is the max amount of sockets you can have on a radial??
as ring is unlimited within 100m 2 right?
Good grief how do you get 2 6mm^ in a BS 1362 socket, 4mm^ is pig enough
Last 2 Victorian terraces I rewired were both 3 storeys with cellar.
Nightmare getting rings up the old studs so 4mm radial power for each floor.
I am using radial power more and more, better future proofing for DIY idiot!
I've never figured out the reason for the British love affair with ring circuits. Surely radials have many advantages....?
It is just the case of old habits mate. It was invented just after the war as folk lore tell for when copper was in short supply. I was brought up on ring final circuits but have to admit I personally prefer radials purely from the testing and fault finding side of things.
Like all things I suppose it is a matter of picking the best design for a particular installation
Someone on the thread, says they wire 6mm radials? In the past socket outlets and the like had cable terminal sizes of 12mm but i'm sure that has since been reduced to 10mm.. If that is still so, you'll have a job wiring a radial circuit in 6mm T&E!! ...Not without a hair trim anyway, ...lol!!!
Quick One
domestic spark,
cbw,